This is a 1989 unit that finally bit the dust. It has served us well but it’s time for a new one. I believe it’s a 4 ton but I don’t know the BTUs of the system. I would like to get the equivalent of what we had. Any help would be appreciated 

Comments

  • pecmsg
    pecmsg Member Posts: 6,023
    edited September 2023
    Get an accurate heat load loss performed. 
    Has the duct static pressure been tested?

    most systems I see are oversized on undersized ducts. 

    When hot and humid how often did it cycle?
    mattmia2
  • JUGHNE
    JUGHNE Member Posts: 11,401
    Lennox manual indicated the 511 having a max output of 4 tons.

    Being installed in 1989 it is most likely oversized.

    And under ducted as stated above.