Plummer used PEX-B when he replaced our indirect water heater, is this wrong?
RedRancher
Member Posts: 1
We had our old Vaughn Top Performer 70 Gallon Indirect water heater replaced. Since it lasted us 22 years and worked well we went with the same unit since they still make it. However, this time our plumber connected all connections to the top of the tank with PEX-B and then used PEX to copper fittings to connect back to the existing 4 copper pipes (from furnace, to furnace, cold water feed, hot-water output).
Just curious if the use of PEX is correct in this install? Again it is an indirect hotwater heater which doesn't make heat just more of a holding tank with no combustion or heat source.
Thank you in advance.
It is fine as long as the type of pex b used on the boiler side has an oxygen barrier unless there is some specific local code prohibition.0
pex b used on the boiler side has an oxygen barrierWhy such a large capacity indirect? Regulated by a sensor or aquastat? Do you have a thermostatic mixing valve on the supply of hot water to the faucets?0
Does the pex say O2 or Oxygen barrier on the markings?
I’ve yet to see any pex B with an O2 barrier in our area.
You’re also not supposed to connect pex directly to a water heater. It should have 18” of non ferrous metal piping before transitioning to pex.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
what is the reason for not connecting pex directly to a water heater0
If the pex is on the boiler side of the indirect it needs to have an oxygen barrier (it will usually be written somewhere on the pipe, "barrier" or something similar), if it is on the plumbing side it doesn't need an oxygen barrier. Pex-b is not enough information to discern if this is the correct application for the product unfortunately, as pex-b comes in both barrier and non-barrier styles0
Normal heaters, I think the rule is in place to keep people from putting pex right next to a drafthood.
Uponor allows it to be installed directly to electric heaters etc, but not next to a drafthood.
Code in many areas still won't allow it due to the possibility of someone misunderstanding the rules.
That's the understanding I have of it. None of this applies to an indirect.
Pex can handle I think, up to 200F at some reasonable pressure.
Please post a picture, I'd like to see the install before commenting. Pex may be rated for 200 degrees but I've seen it get soft passed 180...a bit discomfiting. Mad Dog 🐕0
Yes Of course on the temps. Exactly what I'm thinking Ed, sounding like a Frankenstein install. I've seen that some guys, once they go PEX or Press, will use it exclusively, even where its really not called for or appropriate. I'd just like to see a photo. Mad Dog 🐕1
Pex will be able to handle the pressure and temperature. It reduced flow rates a bit with smaller inside diameter.Bob "hot rod" Rohr
In my neck of the woods you can install pex right up to an indirect or electric water heater, but it must be 18 inches from the heater for gas, so this would be fine (again, in my neck of the woods, not everywhere).
As far as oxygen barrier vs not, for the two pipes connecting the home potable water supply (cold in, hot out to the house) don't need to be (in my understanding) but the two going to and from the boiler (which runs through a heat exchanger in the indirect) should be oxygen barrier so that you are not introducing air into your boiler loop. Will 4 feet of pex b introduce enough air to cause major problems? I can't say, but it's not proper.
Around here even Menards (big box store) sells barrier pex for heating applications.
I'd check the pipes and see if you can see any markings to suggest it's barrier and then just simply reach out to your plumber and ask nicely. "Hey, I can't tell if this pex is oxygen barrier where it ties into the boiler, can you clarify for me if that was used as it is my understanding it needs to be.."