Low flow hot water
ortho1121
Member Posts: 3
I have a gas fired Rinnai hot water heater. I was told it requires at least 1.5 GPM in order to trigger the unit. No problems with showers/high flow but how do I maintain hot water in a low flow situation such as a bathroom sink or washing dishes?
Looking at a few Rinnai spec sheets, it looks like it is more like .5 gpm. There are some types of flow switches that collect magnetic contaminants and fail over time until they are cleaned. Is this a new problem or has it happened ever since it was installed?
A recirculation pump is a way to artificially maintain the minimum needed flow.1 -
It has been since day one. I first changed out the flow restrictors in the showers but otherwise seem to have this low flow problem. I do flush the unit yearly. If I install a recirculating pump will that cause the unit to continually turn on?0
You could consider a tiny tank or two - they make them in the 2 to 8 gallon range that you can use for the lowest flow applications.0
Get a Magnetic Filter like a Boiler Mag or Caleffi and a small ECM re-circulator that is tied to a time clock and Aquastat. You will get hot water flowing through your plumbing system but only when you typically use it and only when the return water temp drops during that set time. You will have a nice efficient system.Nick Ekdahl, CPD, GPDDirector of Training & EducationDawson Company0
Rinnai water heaters require .4-.6 gpm to ignite initially, and .26gpm to maintain the flow of hot water. I would venture a guess and say either your overall water pressure in your home may be too low, or the flow sensor on the water heater itself is failing and ohming incorrectly. put a gauge on a hose bib or anything similar. if pressure is lower than 50lbs i would address that first and move on from there.Experienced Boiler Mechanic In Summit County, Colorado.0
Ah... if our OP is on a private well, it's likely that the well operates between 30 and 50 psi, although a few are set up for 40/60. In which case, a reading below 50 psi is entirely normal. It ain't broke. Don't fix it. Look elsewhere.Br. Jamie, osb
I agree, but with modern flow rates on faucets combined with required flow rates on modern tankless heaters it can cause the flow sensor to not detect enough flow when only 1 faucet is being used at 40-50lbs. which is why they should know house pressure before they start throwing money at the problemJamie Hall said:Ah... if our OP is on a private well, it's likely that the well operates between 30 and 50 psi, although a few are set up for 40/60. In which case, a reading below 50 psi is entirely normal. It ain't broke. Don't fix it. Look elsewhere.
Experienced Boiler Mechanic In Summit County, Colorado.0 -
Oh I quite agree. The modern low flow rate faucets and showers can be a real problem on private systems, particularly when combined with modern tankless heaters which won't work at low flow rates.SummitMechanic said:
There are several workarounds, none of them really good. The one I use is to take the flow restrictors out of anything advertised as low flow -- or avoid buying it in the first place. That is not always possible. I'd also avoid tankless heaters, but only partly for that reason (those things are power hogs). The other is to boost the pressure switch settings, but the pump may not be able to do that and even if it can, it's pretty tough on the pump, and reset the pressure tank pressures to match.
The first option is the best.Br. Jamie, osb
Also, on the models that are high efficiency, like the RUR models, they need higher water pressure because of the internal pressure drop of the unit. If I remember right, it is at least 50 psi.
Rick0