Replacing 1/2 iron with 1/2 copper good idea?
sixplex
sixplex Member Posts: 159
edited August 2023 in THE MAIN WALL
So this rad isn't heating too well.
Up top is 1/2 iron is connected to 1/2 copper below
Copper is about 15% smaller on the inside.
Will replacing 1/2 copper with 3/4 copper give more btua to the rad?
I'm thinking the five 90 degree elbow fittings dont help either, only 2 are needed.
    Steamhead Member Posts: 18,326
    Do the other radiators on that system have the same size pipes?
    Consulting
  • sixplex
    Depending on rad size either 1/2 iron or 3/4 iron, this is the only piped with copper. Why?
  • STEVEusaPA
    First figure out why 'it isn’t heating too well'.
    Is the pipe clogged? Low on system water? Air bound? Shut off valve issue?
    hot_rod Member Posts: 27,112
    Any idea how many btus you need?  That is how you want to size the piping
  • sixplex
    Cleaned out a bunch of sludge from it
    It's a single pipe system, air vent is on the low side of the rad, changing that, might be air bound a bit
    Currently trying to figure if the repiping with a bigger pipe will have a positive impact, being a monoflow system, a pipe that is 15% smaller than designed, with unnecessary elbows makes a difference, just don't know how much of it.
  • sixplex
    edited August 2023
    Someone put that 1/2 copper in, original design was 1/2 steel which is 15% bigger, that's how many btus i need i guess
    mattmia2 Member Posts: 16,080
    What kind of expansion tank does the boiler have, is it a compression tank or a diaphragm tank?
    What kind of air elimination do you have at the boiler?
    Given the number of questions you have about this emitter doesn't heat very well i suspect either you don't have a circulator with enough flow on the monoflow loop or your air elimination isn't very good or both.
  • ChrisJ
    ChrisJ Member Posts: 17,165
    I've never heard of copper pipe having a smaller ID than steel / iron pipe?
    1/2" copper pipe is slightly larger than 1/2" ID.  Especially type M.
    Rich_49
    Oh, and that baseboard is going to have far more resistance to flow than the original standing cast iron radiator did.
    EBEBRATT-Ed Member Posts: 19,932
    edited August 2023
    @sixplex
    You need to find out the btus of the radiation. That is how you size the pipe. Measure the length of the baseboard. 1/2" copper will carry 1.5 gpm which equals 15000 btu. Your baseboard does not likely need that many btus.
    The pipe size and material is probably not the problem and replacing it with 3/4" probably will not help. If it is a 1 pipe Monoflo system, you need two Monoflo tees one on the supply and one on the return and it needs to be piped right.
    Its probably copper because it was an addition to the original system and maybe it was not installed right
    The baseboard will also heat and cool much faster than the standing cast iron radiators so while the areas with the original radiators are still heating the areas they are in with their residual heat, this area will have stopped heating so you likely will not be able to balance this area with the rest of the system, especially since it is monflow.
  • sixplex
    This radiator is the same all the the others in the system, cast iron baseboard type
  • sixplex
    edited August 2023
    1/2 copper ID 0.569 for M, 0.545 for L.
    1/2 iron schedule 40 (seems to be the most common) ID .622
    So the copper has 12.37% smaller ID than the iron.
    I visually compared at the home depot, seems about right
    1/2 iron seems to be equal to 5/8 copper (id) but 5/8 ID copper isn't a thing in canada, only 3/4
    ChrisJ
    1/2” copper almost fits inside 1/2” schedule 40 pipe, so it is a smaller OD and ID
    Same with 3/4, that is how urinal nipples work and some tub spouts
    ChrisJ
    Are your posts about the emitters that don't heat about a different system? Or are those the only standing cast iron radiators on the system?
  • sixplex
    It's a small apartment building 6 units, all apartments have cast iron baseboard rads, and there are 3 free standing rads in the common hallway, 1 of which doesnt heat at all. The one that doesn't heat is on a different return than the rad in this thread they arent related
    So the cast iron radiators are on a separate thermostat from the baseboard?
  • sixplex
    They are all cast iron. Baseboard ones are cast iron too. The free standing one that doesn't work is on a separate thermostat from the baseboard cast iron in this thread
    They are all cast iron but the ci baseboard has a lot less mass than the standing ci so if they were all run off a t-stat sensing the temp in a room where there was ci baseboard it probably wouldn't run long enough cycles for the standing ci to heat, but they are separate t-stats so that isn't part of your problem.
  • Rich_49
    Rich_49 Member Posts: 2,785
    IF i could interject with a question ? In all the years I've been doing this and my descendants before me , I cannot recall ever seeing either baseboard ( copper or Cast ) or radiators that were sized for anything other than 1 gpm . Temps vary for sure but always 1 gpm . 1/2 copper should be sufficient correct ?
    732-751-1560
    Rich McGrath 732-581-3833
    I would  guess 1/2” system's are flowing 1- 1-1/2 gpm. It depends on what the circulator is capable of and the head of the circuit
    most all baseboard outputs charts show 1 and 4 gpm
  • Rich_49
    With a disclaimer about guaranteeing 4 gpm and if that cannot be guaranteed you must use 1 gpm . Did not Siggy say using the extra power and such to have such a minimal gain in output was never truly worth it , or something to that effect ? Maybe that was just on the Mastering Hydronic Design courses .
    732-751-1560
    Use higher flow rates, above 1 gpm all the way to 4 gpm, if for some under-designed reason the 1 gpm is not meeting the load. It's the number they tested and certified to at IBR, once upon a time. I'm not sure who chose it or why?
    With todays ECM 100- 120W would move plenty of flow if you had to run higher gpm for extra output.
    4 gpm, if you need to run that much flow in a 3/4" circuit is still in a comfortable flow velocity.
    I'm not suggesting you design around 4 gpm, the number is shown in most all radiation charts as a guide to what you get and what it cost in additional pump requirement. Certainly flow rates between 1 and 4 could be considered it's not one or the other.
    Rich_49