E20 purge running constantly
hyper1also
hyper1also Member Posts: 2
I awoke to boiler purge running constantly. Only way to stop it was turning power off. I noticed pilot light was off and tried to get pilot lit while power off . No good. Changed out thermocoupler hoping to get lucky. No good. What have I got going on and what do I need to do. I have had a 14 year run on this burner. Thanks
    Steamhead Member Posts: 18,324
    @hyper1also , first thing I'd check is the thermostat circuit. A short in this circuit will make the burner run continuously. Disconnect one of the thermostat wires- if the burner stops, that's your problem.
    What boiler is this E20 installed in?
    Consulting
  • Tim McElwain
    Tim McElwain Member Posts: 4,658
    The relay contacts on the burner tray may be stuck. Contact R.L. Gourley, 80 Felton St. Waltham. Ma.
    781-894-9500 Do you have the manual for the burner if so the part number will be listed in the parts section. If you have further questions Call Tim McElwain 401-437-0557