Oil Hot water furnace PSI over 30
Kailerfey
Member Posts: 8
in Oil Heating
First of all, please excuse my ignorance as this is not my area of expertise!
I have a Dettson hot water furnace that's system psi has been steadily creeping up and over 30 psi (should be 12) and setting off the pressure release valve. I have managed to relieve the pressure by draining the expansion tank but it just keeps going back up to 30+ within a few hours. Even when the furnace is manually shut off. The only way to stop the pressure from increasing is to literally shut off my water.
I can provide any additional details but I figured I'd start somewhere!
Thanks so much in advance!
DJD775 said:Sounds like you either have a leaking domestic water coil or a bad pressure reducing valve. If the problem is happening when the boiler is off you can rule out a bad expansion tank. Either way, call a pro and have them come out and properly diagnose it.
I tried turning off the lever that let's hot water come directly to my tap upstairs and it seemed to stop the pressure from increasing. Could this mean the pressure relief/reducing valve is not the issue and instead narrow it down to being the leaking domestic water coil?0 -
HomerJSmith said:When you fix it be sure and replace the Pressure Relief Valve.0
Right. There should be a valve to isolate the tank from the rest of the system. Close the isolation valve, then open the drain valve. Leave the drain valve open for a while. It will gulp, glurg, and burp for awhile while all the water drains out.pecmsg said:Did you Completely drain the tank or just lowered the pressure?
Then close the drain valve, and open the isolation valve connecting the tank to the rest of the system.
Right. There should be a valve to isolate the tank from the rest of the system. Close the isolation valve, then open the drain valve. Leave the drain valve open for a while. It will gulp, glurg, and burp for awhile while all the water drains out. Then close the drain valve, and open the isolation valve connecting the tank to the rest of the system.0 -
OK, good. I think you have ruled out the tank as the problem. At this point, possible suspects are a failed Pressure Reducing Valve (PRV) that supplies water to the boiler, or a leaking coil for the domestic hot water. (as mentioned a couple posts up by @DJD775 )
To rule out the PRV;
There may be a shutoff valve upstream from the PRV. If you close this valve and pressure still rises, that points to a leaking domestic hot water coil.
If leaking coil, then one possible solution for you is to get a dedicated water heater that is not part of your Dettson.
WMno57 said:OK, good. I think you have ruled out the tank as the problem. At this point, possible suspects are a failed Pressure Reducing Valve (PRV) that supplies water to the boiler, or a leaking coil for the domestic hot water. (as mentioned a couple posts up by @DJD775 ) To rule out the PRV; There may be a shutoff valve upstream from the PRV. If you close this valve and pressure still rises, that points to a leaking domestic hot water coil. If leaking coil, then one possible solution for you is to get a dedicated water heater that is not part of your Dettson.0
Your Dettson boiler heats both the water that heats the house (space heating) and the domestic hot water that goes to the taps.
These are kept separate by the coil. The pressure gauge on the boiler will show the pressure on the space heating side. The pressure on the domestic water side is higher. If the coil has a leak, water from the domestic water system will leak into the space heating side and raise the pressure on the gauge.
If your system has a valve to shut off water to the space heating side of the boiler, domestic water will still be supplied to the coil. If the coil is leaking, the pressure on the gauge will still rise.
The coil is the square to the left of the gauge. The two pipes coming out the top of the Dettson are the inlet and outlet for space heating.
WMno57 said:The coil is the square to the left of the gauge. The two pipes coming out the top of the Dettson are the inlet and outlet for space heating.0
When the yellow valve is closed there will be no water at the hot taps. Pressure on the domestic water side of the coil will drop to zero if a hot tap is opened when the yellow valve is off. Now the direction of leak is reversed. 30 psi on the boiler side will inject stagnant boiler water into your depressurized domestic water system.Kailerfey said:
So it's that yellow valve that is for the domestic. Is it safe for me to shut it off overnight for example while I wait for it to be fixed?
So when the yellow valve is off, don't open the hot taps. Better yet, don't drink the water until your system is fixed and you have run some water through the domestic taps (faucets).