Viessmann Vitorond return temps

mattyc
mattyc Member Posts: 44
The Viessmann vitorond oil fired boiler has an option to use a return port with a special Injection nozzle that is supposed to allow lower return water temperatures.  As per tech support, they stated that the boiler can handle any return temps you throw at it without risking condensation damage to the cast iron.  Anyone have any experience with this?  

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,452
    If that is what they state it should be fine. Check the manual for any low temperature limitations.
  • mattyc
    mattyc Member Posts: 44
    @EBEBRATT-Ed. The manual doesn’t say what temps it can handle but you have to buy an injector nozzle that pipes the return back into the upper side of the boiler as apposed to the bottom of the boiler.  Also you need to use their vitotronic control to do this, as appossed to an aquastat with regular operation.   It sounds too good to be true to have a cast iron boiler handle cold return temps without ruining the cast iron.  I don’t want to test this on a customers new boiler installation lol
    Derheatmeister
  • hot_rod
    hot_rod Member Posts: 22,019
    Nice to see a boiler with 3-1/2" of insulation!
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattyc
    mattyc Member Posts: 44
    @hot_rod. They’re fairly light weight for a triple pass boiler as well.