2 pipe gravity return question
Heat65
Heat65 Member Posts: 10
Could someone tell me about this Webster boiler return trap, never saw one before so I placed my hands in my pockets and backed away.
    EdTheHeaterMan Member Posts: 11,989
    I believe that is a vapor system ore even a vacuum system. Never came across one but others have on this forum. Look at this post from several years ago:
    https://forum.heatinghelp.com/discussion/comment/1506713#Comment_1506713
  • Heat65
    Thanks Ed, if I’m reading the piping diagram correctly the relation to my boiler water line is way off, pictures below.
    Steamhead Member Posts: 18,392
    That's a Webster "Type R" Vapor system, assuming the radiator fittings and air trap are also Webster. The Return Trap is covered in chapter 15 of "The Lost Art of Steam Heating", which you can get from the Store on this site.
    Consulting