Weil Mclain HE 2 boiler not starting
Lukemon100
Lukemon100 Member Posts: 2
I have a HE 2 boiler. The unit has the green (power) light, and the first red light (demand). The circulating pumps runs (I can feel the motor start, and shut off when I turn it off). The third light never lights, but the 4th red light flashes once, then turns off. I am left with the green and one red light. The fan motor does not fire up at all. What does the one pulse (flicker) of the 4th red light mean, and no light on the third.??? Bad fan motor?
  • Lukemon100
    I had a HVAC contractor look at the unit and he said it was a bad control module. I replaced this, and same problem. I won't mention names or use them again. (they wanted 2x the part to replace)
  • neilc
    neilc Member Posts: 3,140
    the blink codes are usually written inside the cover on the labels, or on the device, or in the manual for boiler or device
    known to beat dead horses
  • neilc
    1 and 2 are power and demand,
    what are the labels on 3 and 4?
    "Limit" ?
    and ??
    dark LED is probably limit, and you have an open safety, or??
    post a picture of a wire diagram,
    and LEDs label
  • Jells
    Jells Member Posts: 639
    Do you not have the manual with the diagnostic flow charts? Here it is, hope it helps, worked for me when I needed a new control valve.
    EdTheHeaterMan Member Posts: 11,755
    edited January 2023
    This manual does not have the same boiler control as @Lukemon100 is describing. Must have a later series HE2. I wonder if this is the control supplement that describes the control @Lukemon100 has.https://www.weil-mclain.com/sites/default/files/field-file/he-ii-hsi-control-supplement_1.pdf
    1. When you first get the boiler to turn on, is there a motor operating the combustion fan?
    2. Is there an orange/yellow glow from the HSI ignitor?
    If you don't get this far, then one of the hoses from the pressure switch to the flue box may be clogged with something? It could be water.
    edited January 2023
    Sometimes the barb fittings get clogged shown here with green arrows. Just carefully remove the hose and push a probe in the tiny hole.
  • harry65
    harry65 Member Posts: 1
    great illustration , I tried that and it didn't help. When I turn on the boiler the control module displays one green light and the blower starts, immediately the first two red light come on together and nothing else happen for a minute or two no igniter , then the third red light comes on and it and the green light start blinking any ideas thanks