Pex run length
jtpfarm
Member Posts: 47
I'm finally finishing the floor heat under my subfloor in the house. Our house has a 30x40 open room with 16x20 being carpet and the rest hard floor. As I did between our carpeted bedroom and hard floor bathroom, I'd like to have separate runs under the carpet and hard floor to adjust flow differently.
Here is my issue, if I have a single run under my carpet I'm going to be about 450' including my home runs. I don't have enough room on my manifold to add another run. Is 450' going to be too much with a grundfos 15-58FC pump in my application?
Thanks
Thanks
I push 350-400ft for my garage loop using an Alpha2 on constant pressure mode of 12ft. It flows pretty slow, but it flows.
Your pump will do nearly 19ft at 0.5 gpm on speed-3, and 17 on speed-2.
Currently in building maintenance.0 -
There are 2 issues with the 450’ idea and they are both working against your goal of more heat under the carpet.
1. With 450’, the flow will be greatly reduced.
2. With that much distance (and the reduced flow) your delta t will be greatly reduced and you will have significantly reduced output.
IMO you don’t need a different flow rate to the carpeted area (higher temp would help but that is more challenging)
Albert Einstein1 -
450' with 1/2" pex?Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Zman said:There are 2 issues with the 450’ idea and they are both working against your goal of more heat under the carpet. 1. With 450’, the flow will be greatly reduced. 2. With that much distance (and the reduced flow) your delta t will be greatly reduced and you will have significantly reduced output. IMO you don’t need a different flow rate to the carpeted area (higher temp would help but that is more challenging)0
The carpet is insulation you would think you need more heat under the carpet not less0
@jtpfarm
Slowing down flow will lower overall heat output. Lower flow results in a lower average water temp in a loop which will result in a lower amount of heat being put into the space.
What tube spacing are you using? at 12" centers I show a 350' loop, or 430' approx at 8" centers for that 16x20 space. Using an estimate 25 BTU /sq ft in that carpeted area, estimated carpet as R2 It looks like you need to move only 0.93 GPM on that long 450' loop but you will have 14' head from the circuit head loss only, add the pressure drop from your manifold (approx 2 ft water) so you need to move about 1 GPM at 16' head loss, and that is only for this loop, and not including the added pressure drop from all of your piping fittings and valves. Now you would need to add the flow rates of all connected circuits, this is likely your largest pressure drop, and see if that would work with your pump. (my guess is no, or it will work until you get to design day)
I would cut the loop into two loops, without question but that's just me.
GGross said:@jtpfarm Slowing down flow will lower overall heat output. Lower flow results in a lower average water temp in a loop which will result in a lower amount of heat being put into the space. What tube spacing are you using? at 12" centers I show a 350' loop, or 430' approx at 8" centers for that 16x20 space. Using an estimate 25 BTU /sq ft in that carpeted area, estimated carpet as R2 It looks like you need to move only 0.93 GPM on that long 450' loop but you will have 14' head from the circuit head loss only, add the pressure drop from your manifold (approx 2 ft water) so you need to move about 1 GPM at 16' head loss, and that is only for this loop, and not including the added pressure drop from all of your piping fittings and valves. Now you would need to add the flow rates of all connected circuits, this is likely your largest pressure drop, and see if that would work with your pump. (my guess is no, or it will work until you get to design day) I would cut the loop into two loops, without question but that's just me.
As I said, this is between floor trusses. So I have a down and back run between each set of trusses. So in that 20' are I have 12 spaces between trusses that have a down/back loop.
Thanks for your thoughts so far.0 -
My reasoning for slowing it down was to get the delta t wider and give the run time to transfer its heat into the room. These are running at 160 degrees. But perhaps I'm wrong in that thinking. Maybe I should be slowing down the hard floor instead?jtpfarm said:
A few things can be learned from this graphic. First is the heat output of the 3 various flow rates. It is the AWT average water temperature in the loop that makes a difference inn the heat output.
Also notice the temperature at the end of this 300' loop at the slower flow, wider delta.
You might not want to take advice from anyone that tells you slowing the flow to get more "linger" time in the loop, increases heat output
You'll not get much heat output on the tail end of that longer loop, certainly not at wider delta T operation.
Tighter delta takes a bit more pumping power, with ECM circs it really not much of an issue, if power consumption is a hangup?Bob "hot rod" Rohr
Living the hydronic dream1 -
@jtpfarm
My example is showing a fairly wide delta T for infloor heat at 20 degrees, this is just to show what it would take to heat the space, not built for maximizing comfort. To adjust this for a more usual 10 degree delta T, and take into account that this is joist underfloor heating, with all other estimated parameters the same as my previous post. You would need to pump almost 2 GPM, at over 50' head loss, the 15-58 is too small, but never mind that because the requirements are out of whack. You need to do 2 loops in that space in my opinion
as for the reasoning behind your flow requirements, it is not the case, faster flow will increase the average water temp, which will result in higher output from your emitters, exception to this possibly being large floor standing cast iron radiators which becomes a hot topic of debate around here every now and then
defer to what @hot_rod has said regarding this topic0
- 87K THE MAIN WALL
- 113 Chimneys & Flues
- 106 Geothermal
- 981 Plumbing
- 388 Solar