Steam Main Vent Configuration Question

CKNJ
CKNJ Member Posts: 65
I was looking at my main vent configuration which is an antler (linear) set up. But then an alternative setup occurred to me and I thought i would ask the pros about it, so here goes.

If space between floor joists allows (and in mine it does), could i replace the "T" on which each vent sits with a cross fitting and attach the Gorton #2 vents across from each other using a short nipple and an elbow on each side? From that cross, a 3 inch nipple would connect to the next cross with the same setup for the vents. And of course a plug at the end. It seems to me a configuration like this would considerably shorten an "antler" set up and allow each vent to be removed individually if replacement is needed.

Is there any particular reason a setup like this would not work?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 25,934
    If you've got the height, it would work fine.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Waher
    Waher Member Posts: 335
    I've always wondered if exceeding 10" in height above a main for a vent creates an issue of not since the recommendation to avoid water hammer & debris damage for main vents is 6-10" in elevation.
  • Jamie Hall
    Jamie Hall Member Posts: 25,934
    That recommendation is a minimum -- not a maximum or range
    Br. Jamie, osb