Lochinvar Install- Gravity Feed settings
Reynz_2
Member Posts: 98
Should the circulator be set at it slowest setting on an original gravity feed system? I've been told the new circulator will have 3 settings, low, med, high. I'm thinking that with a original gravity feed piping with iron baseboard that I should set it at low, rather than med or high? Certainly I plan on settings that require it to run as long as possible and avoid short running, just interested in circulator settings. From what I have learned before, it is better to have water move rather slowly through the baseboards rather than speed through. Where is Floyd when you need him? Lol
Nevermind- what a topic, seems it never goes away. No response needed on this one! Lol0
"No reply needed" sounds like what I got for my son-in-law for his birthday.
@Reynz_2
You may need to experiment to get the house to heat evenly. Does the house have a boiler with gravity circulation now or is it pumped?0 -
Im running a converted gravity system in a single loop with TRV on all radiators. Ive set the Alpha2 circulator on constant speed level 1. Moves 7-8 gallon minute which matches up closely to the boiler rating of 80KBTU. The circulator consumes 8 watts power at that setting, amazingly efficient.I’ve got the ODR curve pretty well dialed in, boiler routinely runs for 7-8 hours after coming off 2 degree setback at 5am. Takes about 1.5 hours to get inside room temperature to 71F from 69F but then keeps running for hours. My temperature curve is set to 86F SWT @ 68F outside temp up to 116F SWT @ 0F outside temps. The 3100SFT house is over radiated with 17 radiators on top two floors plus two in basement shops.0
I'm not sure which Lochinvar boiler is being talked about, but with their condensing boilers they supply a 0-10 VDC pump to be used as the boiler pump which responds to a sensor attached to the mixed secondary piping. The secondary pump is supplied by the installer.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
- 121 Chimneys & Flues
- 15.8K Strictly Steam