Heat loss formulas and questions
Pulse
Member Posts: 78
U VALUE = 1 / R VALUE(0.2 * INCHES(SLAB THICKNESS))
DELTA T = INDOOR TEMP - GROUND TEMP
HEATLOSS = U VALUE * SQ FT * DELTA T
Is the above formula correct to calculate the heat loss through a slab? I have a 4" uninsulated basement slab. For just under a 400sqft basement, I have a BTU loss of ~9500, in the concrete slab alone. That seems extremely excessive?
Air infiltration using area
CFM50 = BLOWER DOOR TEST
CFH = CFM50 / 20 * 60
DELTA T = INDOOR TEMP - DESIGN/OUTDOOR TEMP
HEATLOSS = (CFH * (ROOM EXTERIOR SQ FT / HOME EXTERIOR SQ FT)) * DELTA T * 0.018
Air infiltration using volume
ACH50 = CFM50 / TOTAL HOME VOLUME * 60
ACH(NATURAL) = ACH50 / LBL FACTOR
*OR*
ACH(NATURAL) = ((CFM50 / 20) * 60) / TOTAL HOME VOLUME
HEATLOSS = ROOM VOLUME * DELTA T * ACH * 0.018
Which air infiltration formula should I be using or is there a better one? I am relying on a CFM50 value from a blower door test done 10 years ago. Is it possible to calculate without the blower door test?
*OR*
What temperature difference did you use for the basement floor? Are you heating the inside to 70 deg. The floor temp won't be 0 it will probably be in the 40s or 50s. That will affect your calculations so your TD will change0
If you have the fuel usage, you can calculate heat loss that way too - you’ll be looking at what actually occurred that way0
@EBEBRATT-Ed
@Hot_water_fan
1.25(U) * 380(SQFT) * 20(70 indoor - 50 ground temp ) = 9500 BTU
Right now there are 3x 4' electric baseboards down there. They do not run constantly/excessively. I just want to make sure I do not create a sauna down there when I size my panel rads.
The boiler will also be down in that area, should I subtract a certain amount of BTUs for it?
What are the baseboards rated? Turn two off and see how it does.0
The 10 year old blower door test is probably a better number for infiltration than you would get trying to guess.0
240/1000, so i guess ~3400 BTUea, so maybe i was overthinking thisHot_water_fan said:What are the baseboards rated? Turn two off and see how it does.
My main concern is just the air infiltration then, if I am calculating that properly0 -
What’s the fuel usage? The odds of a heat loss calculation of the manual J variety coming in undersized are slim. And the smallest boilers are usually much bigger than the typical load.0
the load @ 72 inside temp:Hot_water_fan said:What’s the fuel usage? The odds of a heat loss calculation of the manual J variety coming in undersized are slim. And the smallest boilers are usually much bigger than the typical load.
~32K BTU @ 20 degrees outside
~37.K BTU @ 7 degrees outside(design)
Boiler will be an 85k(79k actual, 8500 min fire)
I know you shouldnt size for the indirect, but i was thinking about a 110k boiler. It brings my GPM recovery up to 2.25(101K) vs 1.75(79K). The min fire would be 11K vs 8.5K
Actually, you should always size to the largest load. If you want high performance indirect capacity, the boiler needs to cover that.
In todays well insulated, efficient homes, the DHW load is often the largest load.
The mod cons are much better suited to zoned systems compared to fixed output boilers in most all cases.
It's rare to see a standard 110K cast boiler turn down to 11K
What’s being overlooked in calculating the slab is that up to 60% of the heat loss is at the edge and perimeter.
With a 70* delta T, you should use 56.7 btus per lineal foot with no edge insulation or 14.7 btus per lineal foot with 2” of edge insulation.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
oh, good to know, but I would be buying a mod con.hot_rod said:Actually, you should always size to the largest load. If you want high performance indirect capacity, the boiler needs to cover that.
For me that would be ~59' * 56.7 = 3345.3 BTUIronman said:What’s being overlooked in calculating the slab is that up to 60% of the heat loss is at the edge and perimeter.
I am now at:
9500 BTU - slab
3300 BTU - slab edge
2600 BTU - windows/exterior walls/air
15400 BTU loss for a 380 sqft finished basement, that equals the heat loss of my other 1600 sq ft of living space..lol
seems incorrect..
15400 BTU loss for a 380 sqft finished basement, that equals the heat loss of my other 1600 sq ft of living space..lolFor sure ! Just use your fuel usage, these calcs are not getting you anywhere.
seems incorrect..0 -
I am sorry, but what do you mean fuel usage?Hot_water_fan said:15400 BTU loss for a 380 sqft finished basement, that equals the heat loss of my other 1600 sq ft of living space..lolFor sure ! Just use your fuel usage, these calcs are not getting you anywhere.
seems incorrect..
I have electric heat currently0 -
Pulse said:
Actually, you should always size to the largest load. If you want high performance indirect capacity, the boiler needs to cover that. In todays well insulated, efficient homes, the DHW load is often the largest load.
oh, good to know, but I would be buying a mod con.What’s being overlooked in calculating the slab is that up to 60% of the heat loss is at the edge and perimeter.
For me that would be ~59' * 56.7 = 3345.3 BTU I am now at: 9500 BTU - slab 3300 BTU - slab edge 2600 BTU - windows/exterior walls/air 15400 BTU loss for a 380 sqft finished basement, that equals the heat loss of my other 1600 sq ft of living space..lol seems incorrect..
With a 70* delta T, you should use 56.7 btus per lineal foot with no edge insulation or 14.7 btus per lineal foot with 2” of edge insulation.No, just use the edge calculation for the slab.Bob Boan
@Ironman
Ah, alright only use edge
So where did you get your figures. The only formula I can find is:
F-factor * Perimeter * Delta T
For F factor, I found two charts, one said .73 for uninsulated, the other went by climate zones, which for my zone 5 is: .54
.73 * 59' * (72-20) = 2239 BTU
.54 * 59' * (72-20) = 1656 BTU0