What am I looking at here?
AK_TK
AK_TK Member Posts: 1
Can anyone help identify what this is? All I have been told is that it is installed on a hydronic heating system here in Alaska.
  • bburd
    bburd Member Posts: 1,242
    That is a flow control valve, a weighted check valve. It stops heat from rising out of a boiler by gravity flow into a hot water radiator system after the thermostat stops calling for heat and shuts off the circulator pump.
    The normal setting is in the middle, marked “winter”. If the lever is set to  “open”, the valve will stay open and gravity flow will be allowed; this is useful if a circulator pump fails, some heat will still be provided. If it is set to “closed” heat will not circulate.
    Bburd
    AK_TK
    Steamhead Member Posts: 18,185
    The lever on that one has been broken off. It used to point to where it says "Open", "Winter" and "Close".
    Consulting
    EdTheHeaterMan Member Posts: 11,550
    edited December 2022
    If the system is operating properly, then the broken handle would be pointing to WINTER
    Here is a short description of Flow Control Valves on page 8 of this
    booklet https://www.xylem.com/siteassets/brand/bell-amp-gossett/resources/technical-brochure/fh-z100b-bg-zoning-made-easy-2.pdf
    Flo-Control Valves Control Overheating,
    Not the Flow!
    Maybe “Flo-Control” was a bad name to give to this device back in the
    old days when we were converting gravity hot-water systems to forced
    circulation. The industry needed something that would stop the
    hot water from rising up into the radiators when it wasn’t needed.
    Hot water will do that, you know. It’s lighter than cold water.
    But the name Flo-Control valve makes some guys think they can
    balance a zoned system by turning the top levers on the valves.
    That’s not what those levers are for.