steam condensate

creger.robert
Member Posts: 89
please see following
pumps keep getting air locked-any thoughts

pumps keep getting air locked-any thoughts


0
Comments
-
We've had issues with similar pumps when used as boiler feed pumps. Any grit (rust, etc) will wreak havoc.
Is there a real fine strainer on the inlet side of the pumps?0 -
For simple sump lift pumps, (not really different than your steam Pedestal pumps), a 3/16 hole drilled in the discharge line just above the water line is recommended to avoid this. FWIW0