Wiring/controls help
tekmar356
https://www.watts.com/products/hvac-hot-water-solutions/controls/boiler-mixing-controls/356/356
scroll down to Installation and Operation - 356 (Sep 2008 - Present)
https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/42849-source/356-d-06
taco zvc 404 zone valve control box
https://www.tacocomfort.com/documents/FileLibrary/102-399.pdf
One Pipe System0 -
This throws some installers off. You need a transformer to power the control,then two wires to the zone control to signal it on with any heat callBob "hot rod" Rohr
Here is the total package
1. Taco ZVC gets a call from a zone.
2. Zone valve opens. Zone valve end switch signals ZVC to call for heat mode
3. ZVC end switch at bottom X X (or C and NO) activates P3 system pump
4. ZVC end switch at top X X sends signal for a call for heat to the 356 at D1 in the 356 diagram.
5. 356 operates the injection pump P2
6. 356 signals boiler to operate
7. Boiler controls operate P1
You guys are awesome thanks for the help!!0
Could the 24v come from the relay box instead of another separate transformer? Shouldn’t take much to power the tekmar?EdTheHeaterMan said:Here is the total package
You may be correct. LCD for the front, Relay for the boiler and a potentiometer for the injection pump. I guess it depends on the quantity and type of zone valve and the size of the transformer in the Tacohot_rod said:
Could the 24v come from the relay box instead of another separate transformer? Shouldn’t take much to power the tekmar?Edward Young Retired