Wiring/controls help
Comments
-
tekmar356
https://www.watts.com/products/hvac-hot-water-solutions/controls/boiler-mixing-controls/356/356
scroll down to Installation and Operation - 356 (Sep 2008 - Present)
https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/42849-source/356-d-06
taco zvc 404 zone valve control box
https://www.tacocomfort.com/documents/FileLibrary/102-399.pdf
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
This throws some installers off. You need a transformer to power the control,then two wires to the zone control to signal it on with any heat callBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Here is the total package
1. Taco ZVC gets a call from a zone.
2. Zone valve opens. Zone valve end switch signals ZVC to call for heat mode
3. ZVC end switch at bottom X X (or C and NO) activates P3 system pump
4. ZVC end switch at top X X sends signal for a call for heat to the 356 at D1 in the 356 diagram.
5. 356 operates the injection pump P2
6. 356 signals boiler to operate
7. Boiler controls operate P1
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
You guys are awesome thanks for the help!!0
-
Could the 24v come from the relay box instead of another separate transformer? Shouldn’t take much to power the tekmar?EdTheHeaterMan said:Here is the total package
1. Taco ZVC gets a call from a zone.
2. Zone valve opens. Zone valve end switch signals ZVC to call for heat mode
3. ZVC end switch at bottom X X (or C and NO) activates P3 system pump
4. ZVC end switch at top X X sends signal for a call for heat to the 356 at D1 in the 356 diagram.
5. 356 operates the injection pump P2
6. 356 signals boiler to operate
7. Boiler controls operate P1
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
You may be correct. LCD for the front, Relay for the boiler and a potentiometer for the injection pump. I guess it depends on the quantity and type of zone valve and the size of the transformer in the Tacohot_rod said:
Could the 24v come from the relay box instead of another separate transformer? Shouldn’t take much to power the tekmar?Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements