No heat 40 year old peerless gas boiler
nikki2561
nikki2561 Member Posts: 6
Pilot is lit no heat kicking on..just changed the low water cut off and changed the gas valve..still no heat coming on...the fan also runs.can anyone help?
  • GGross
    GGross Member Posts: 1,589
    Have you confirmed that you have a call for heat? As in not just turning up the thermostat but testing at the TT terminals that you actually have a call for heat? Is there an open limit, or any other external safety device on the system that may block burner operation?
    EdTheHeaterMan Member Posts: 10,871
    What type of boiler do you have? Peerless made many different boilers 40 years ago. If we limit it to the ones that have a standing pilot, there may be about 7 or 8 different models.
    1. Can you post a picture of the boiler rating plate or sticker that has the model number
    2. Can you post a picture of the heater from far enough back to see what the heater and the connecting pipes look like
    3. Does this boiler make steam for the radiators? OR
    4. Does this boiler make hot water that gets pumped through the radiators?
    5. Can you identify or take a picture of the FAN the is running?
    6. Does this fan stop running if you turn the thermostat as low as it can go? (so there is no call for heat)
    mattmia2 Member Posts: 13,841
    If we're just randomly guessing without any information, this is about the right age for vent dampers.
  • JUGHNE
    JUGHNE Member Posts: 11,481
    What fan would be on a 40 year old boiler with standing pilot?
    Side wall power vent??
  • nikki2561
    It's is a G-561-SP
  • nikki2561
    edited November 2022
    this is steam heat..fan does kick off when lowering the temp below house temperature
  • nikki2561
    I can get more information and pictures tomorrow and post them in thank everyone for replying this far
    109A_5 Member Posts: 2,578
    Hello @nikki2561,
    An inexpensive Multi-meter may have been a faster, more economical solution to finding the defective device on your boiler. The random parts changing (Parts Cannon) technique rarely is the best way, as you are finding out the hard way.
    Safety limit devices, Roll out switch, Spill switch, Power Vent safety devices.
    Pressuretrol switch, plugged pigtail.
    All could be an issue.
    109A_5 said:
    Hello @nikki2561,
    Also, now they need a tech that understands combustion to set up the new valve in addition to the original problem.
    109A_5
  • nikki2561
    Everything has been checked with the meter..even tried jumping the furnace at the actual furnace and at the thermostat furnace just won't fire...this is also power vented
  • JUGHNE
    The tstat usually starts the fan first, then the fan has to tell the boiler that is is running.
    This is most likely done with a pressure switch connected with small tubing.
    When that switch closes it would send power to the gas valve.
    This may or may not be your situation.
    There may be a wiring diagram on the door of the boiler.
    Can you post a picture of that is so?
    Also a picture of the fan, boiler controls etc.
    Back up a little with the camera.
    nikki2561
    Hello @nikki2561,
    If everything was checked with a meter you would know where the problem is, assuming it is actually an electrical issue. Assuming it is a 24 VAC system, if there is not 24 VAC at the Gas valve when the thermostat is calling for heat you have not checked everything. Or the person using the meter does not know what they should be doing. The electrical circuitry on a boiler that age is not very sophisticated. It should only take a few minutes (if that) to find an electrical defect.