Boiler only firing on for one of two heating zones
lbeachmike
lbeachmike Member Posts: 215
I'm sure this is a simple issue. I can see on the Taco switching relay that the Zone 1 thermostat is calling for heat, but the boiler does not fire on. If I call for heat from Zone 2, the boiler fires on. Is this simply a bad Taco switching relay?
    hot_rod Member Posts: 27,419
    take a pic with the cover off, to see how it is wired.
  • SteveSan
    SteveSan Member Posts: 298
    @lbeachmike if you are in front of the control give Taco Technical Services a call 401-942-8000 we are hear until 5pm today and can help you with your issue.
  • Joe Mattiello
    Joe Mattiello Member Posts: 751
    Try to validate demand by placing a jumper across Rand W on the control
    if zone two is closing isolated endswitch to engage boiler, you might have a faulty thermostat
    Joe Mattiello
    Taco Comfort Solutions
  • lbeachmike
    It turns out this is a blower relay issue. My diagnostics were premature because of lack of knowledge. The boiler actually was firing on, but after the water was at the needed temps it didn't need to fire on again - we have hydronic forced air, so I didn't realize the blower had its own separate logic for it to fire on. I've always been around HW baseboard, or steam heating, so I was more used to how those systems would operate.
  • Joe Mattiello
    Glad you figured it out! Stay warm and thanks for using Taco
    Joe Mattiello
