Pipe size for shop
Geno00
Member Posts: 1
in Gas Heating
Just purchased a house with a nice size 40 x 56 shop and want to put a furnace in the shop. My gas meter is 250 feet away. What size of gas line is needed to be ran to the shop to cover the furnace and one water heater? Thanks
https://forum.heatinghelp.com/discussion/comment/1719537#
This thread might helpEdward Young Retired
If natural gas, using schedule 40 metallic pipe with an inlet pressure less than 2.0 psi and a pressure drop of 0.5 w.c., I use the tables in the Uniform Plumbing Code (2009). All you have to know is your total demand (now and future) in BTU's.
If your gas provider will supply gas at a higher pressure, your pipe size can be reduced, but you will have to install regulators at your appliances.
If propane, that's a different table and the pipe size will be smaller.
this is the part of the aforementioned thread I thought might help This might help
https://www.youtube.com/watch?v=1fpy9NrE21c
