Just purchased a house with a nice size 40 x 56 shop and want to put a furnace in the shop. My gas meter is 250 feet away. What size of gas line is needed to be ran to the shop to cover the furnace and one water heater? Thanks
0
Comments
-
https://forum.heatinghelp.com/discussion/comment/1719537#
This thread might helpEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
If natural gas, using schedule 40 metallic pipe with an inlet pressure less than 2.0 psi and a pressure drop of 0.5 w.c., I use the tables in the Uniform Plumbing Code (2009). All you have to know is your total demand (now and future) in BTU's.
If your gas provider will supply gas at a higher pressure, your pipe size can be reduced, but you will have to install regulators at your appliances.
If propane, that's a different table and the pipe size will be smaller.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
this is the part of the aforementioned thread I thought might help This might help
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements