Buderus Panel Radiator Measurements
152NP
Member Posts: 49
Can anyone verify if the advertised lengths of Buderus panel radiators include the projection of the flowsetter valve?
I only have 6 feet of wall to pack in a little over 7,000 BTUs of output, and every inch counts. Ideally, I would like to use a 12" high unit. A 20" may not fit under the windows once I account for the space needed at the bottom for piping.
They also suggest these clearances which further complicates things:
Can you remove the flowsetter valves on these radiators and just screw in a plug? The radiator is on a home run system, there are flow adjusters at the manifold, and I am going to be using a TRV, so I don't think I need it. I know you can just screw a TRV on the flowsetter, but, if I need that extra few inches, I can use a Danfos remote setpoint sensor run to a TRV in the supply line somewhere.
Any advice is appreciated.
The TRV needs to be installed over the flowsetter. A 12x64" #22 has an output of 6800btus @190 degrees. I typically size for 140 degree supply water temps because I'm using a condensing boiler. A 16x64" #22 would have an output of 8600btus0
If you can find a plug with the same threads, I don't see a problem with capping off that valve.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
If a plug were installed, the radiator would not have a method of control without the flowsetter modulating the return temperature.0
@Alan(CaliforniaRadiant)Forbes and @Paul Pollets Thank you for responding to my post.
I called Bosch/Buderus technical support, and they said they believed the published measurements were inclusive of the protruding flowsetter valve, and that I could remove the valve if I had another means of controlling the flow, which I do.
In the end, I wound up ordering Ecostyle brand panel radiators. They are less expensive and have a much greater selection of sizes. I got a 16"H x 56"W that is capable of 7,587 BTU at 180 degree supply and will fit within the problem space with room to spare.
For what it is worth, I am running a mod-con boiler with outdoor reset, and design temp of 180.
Regarding my comment about ditching the built in valve and being able to control the radiator with a remote sensor, here is what I did in one of the rooms of my house. I have a remote temperature control hooked up to a TRV valve in the basement mounted to a joist. It works great:
With the Ecostyle, I have room and will put the TRV control right on the radiator, but will use the kind with a remote temperature sensor as there will be some furnishings in front of it that might prevent it from reading the room temp accurately.
Thanks again!
Some creative connections there
You can get pex compression adapters to clean and cheapen the cost of that creative connection. 1/2" valves would be adequate also.Bob "hot rod" Rohr
Living the hydronic dream0
