Buderus Panel Radiator Measurements
152NP
Member Posts: 49
Can anyone verify if the advertised lengths of Buderus panel radiators include the projection of the flowsetter valve?
I only have 6 feet of wall to pack in a little over 7,000 BTUs of output, and every inch counts. Ideally, I would like to use a 12" high unit. A 20" may not fit under the windows once I account for the space needed at the bottom for piping.
They also suggest these clearances which further complicates things:
Can you remove the flowsetter valves on these radiators and just screw in a plug? The radiator is on a home run system, there are flow adjusters at the manifold, and I am going to be using a TRV, so I don't think I need it. I know you can just screw a TRV on the flowsetter, but, if I need that extra few inches, I can use a Danfos remote setpoint sensor run to a TRV in the supply line somewhere.
Any advice is appreciated.
I only have 6 feet of wall to pack in a little over 7,000 BTUs of output, and every inch counts. Ideally, I would like to use a 12" high unit. A 20" may not fit under the windows once I account for the space needed at the bottom for piping.
They also suggest these clearances which further complicates things:
Can you remove the flowsetter valves on these radiators and just screw in a plug? The radiator is on a home run system, there are flow adjusters at the manifold, and I am going to be using a TRV, so I don't think I need it. I know you can just screw a TRV on the flowsetter, but, if I need that extra few inches, I can use a Danfos remote setpoint sensor run to a TRV in the supply line somewhere.
Any advice is appreciated.
0
Comments
-
The TRV needs to be installed over the flowsetter. A 12x64" #22 has an output of 6800btus @190 degrees. I typically size for 140 degree supply water temps because I'm using a condensing boiler. A 16x64" #22 would have an output of 8600btus0
-
If you can find a plug with the same threads, I don't see a problem with capping off that valve.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
If a plug were installed, the radiator would not have a method of control without the flowsetter modulating the return temperature.0
-
@Alan(CaliforniaRadiant)Forbes and @Paul Pollets Thank you for responding to my post.
I called Bosch/Buderus technical support, and they said they believed the published measurements were inclusive of the protruding flowsetter valve, and that I could remove the valve if I had another means of controlling the flow, which I do.
In the end, I wound up ordering Ecostyle brand panel radiators. They are less expensive and have a much greater selection of sizes. I got a 16"H x 56"W that is capable of 7,587 BTU at 180 degree supply and will fit within the problem space with room to spare.
For what it is worth, I am running a mod-con boiler with outdoor reset, and design temp of 180.
Regarding my comment about ditching the built in valve and being able to control the radiator with a remote sensor, here is what I did in one of the rooms of my house. I have a remote temperature control hooked up to a TRV valve in the basement mounted to a joist. It works great:
With the Ecostyle, I have room and will put the TRV control right on the radiator, but will use the kind with a remote temperature sensor as there will be some furnishings in front of it that might prevent it from reading the room temp accurately.
Thanks again!
0 -
Some creative connections there
You can get pex compression adapters to clean and cheapen the cost of that creative connection. 1/2" valves would be adequate also.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements