Aquastat setting
gyrfalcon
Member Posts: 189
Is this setting correct for 180deg water temp? This is how last company left it.
Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.
So the metal prong is just for the high limit stop?Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
Isn't that the operating limit, not the high limit?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Residential Boiler controls for single family home does not require separate operating limit and high limit controls. If the boiler is located in a public building the AHJ may require a second limit that is set higher than the operating limit. That second High limit may also need to have a manual reset.
The L8148 control that is pictured is currently set at 190° and has a non adjustable 10° differential. So that control will open the burner circuit (shut off the burner) when the water temperature at the probe reaches 190°. When the water temperature drops to 180° the burner circuit will close (Burner fire on) and the burner will fire as long as there is a call for heat from the thermostat or zone control connected to T T of that control.Edward Young Retired
2 -
So to go any lower, I need a different aquastat. It seems some favor electronic versions from Honeywell/ Resideo or maybe Hydrolevel.Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
Boiler has a clean bill of health for this season. Heat exchanger is cleaned up along with inspection and exhaust gas combustion test . Showing 78-80 % efficiency.Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
How can a combustion test show 78-80%?
Sorry for my ignorance in asking, but should I look into this further? Am I missing something? On a 40 yr old lp boiler rated at 82%, the 78-80 % seemed reasonable to me. The tech was here while I was at work and this is what my wife reported to me.Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
Waiting for the stack thermometer to get to steady state and reading this chart can have some room for interpretation. Just one possibility, Steve.
But using the digital meters there should be an exact reading at a specific point in time. That is the number that should be given. Perhaps the LP Gas technician was just offering an opinion based on what he saw on his test equipment at a few different observations during the several minutes the probe was inserted, taking a reading. It appears that those numbers keep changing over the 5 to 10 minutes that the test is performed. That has been my experience anyway.