Electric water heater / Buffer tank
Snowmelt
Member Posts: 1,454
Existing electric water heater Bradford while , I think 32 gallons , can I use that for a Buffer tank with the hot cold for the space loop & the pressure relief tapping and the drain valve tapping for the boiler loop. Of course I would tee it and put the relief valves and the drain on a tee.
So the water heater will be used as a boiler?0
Mr 57, how would that be piped0
Yes it will be used as a boiler although they are doing it wrong it’s acting as a boiler now with no P/S0
Why a four pipe buffer tank at all? You could do a two-pipe buffer tank too.0
Easier with a purpose built buffer tank I’d assume.
So let the water just heat up bottom of tank so it’s in series with the pumps0
I'm not a Pro, this is my guess (greater than sign ">" shows flow direction).Boiler Loop
Boiler Secondary Supply > Water Heater Drain Fitting
Water Heater PRV fitting > Boiler Secondary ReturnSpace Loop
Water Heater Hot > Space loop input
Space Loop output > Water heater cold0 -
What type of flow rate are you considering? You are limited by the 3/4” taps, or the element holes
Ive connected the two top with fip tube removed. For your bottom, you are limited to the 3/4 drain port. I use a 3/4 male C 1-1/4 copper adapter yeti increase quickly
You can also use the element holes, typically 1”, you give up some tanks use ability as the are not top and bottom, 6 or so “ up and down, but a large connection, if you are needing 8 gpm or more, use the element holes
Same method a 1” make X 1-1/4” copper adapter.
Here are a few that I have built. That Viessmann one was 10 or so
years ago
The small 6 gallon has a 4500w element for a 15,000 btu backup heat source
I think this would be better though:Single Loop
Boiler Secondary Supply > Space Loop Input
Space Loop Output > Water Heater Cold
Water Heater Hot > Boiler Secondary Return0 -
What is the space loop? Will the boiler be heating any other loops? Now or future?0
The disadvantage to all this is you get the blame if there is a failure in the existing water heater.
Is the reason for doing this increased buffering capacity or gaining redundant heat sources (WH + Boiler)? Are those benefits worth the additional points of failure?
If your in Massachusetts the water heater as to be specifically design to be used as a heating and domestic hot water source and approved for that purpose by our plumbing board. We replace these type water heaters all the time and its not cheap. These are not long term solutions to your heating system.
These are installed in managed property. We work with the property manger to replace these. The property manager has something like 500 units in multiple locations with the approved water heaters but we are constantly replacing them. As a developer they are cheaper to install initially but the owners pay dearly in replacements.
Use the proper materials and equipment for safe operation of your heating system.0 -
Thermo 2000 makes such a productBob "hot rod" Rohr
The house is sprayed foamed really good. The boiler is large, but I’m going to say no more then 75 total, also he has 2 radiant floor 1 heated rad and 3 high temp. Later I will ask the btu for the high temp. But I know the low temp is 20-30 thousand btu. I can either do what hot rod said do a 3/4 male to 1 inch male. I know there’s less then 100,000 btu for whole house.0
What is your goal for the buffer tank? Longer boiler cycles?Bob "hot rod" Rohr
Yes he has small zones. Even a towel warmer as a zone , but as you can see it’s not the most organized job0
- 50 Industry Classes