What nozzle type
conrajetken
Member Posts: 10
in Oil Heating
Can anyone tell me the proper nozzle angle and pattern (A,
for a Weil McLain A-B-468V-W boiler. Thank you!
Burner type?0
And pump pressure.
If your Weil McLain 468 boiler has a Beckett AFG burner you can use a 1.25 GPH 80° A (hollow) nozzle at 100 PSI. You will want to check the burner head to make sure it is the F-6 and there is a 2-3/4" static disk on the nozzle assembly.
If your Weil McLain 468 is equipped with a Carlin EZ-1 burner then you would use a Delavan 1.25 70° B (solid) nozzle at 100 PSI.
If your Weil McLain 468 is equipped with s Carlin CRD 99 burner then you would use a Hago 1.25 60° SS (semi-solid) nozzle at 100 PSI.
Many of the later Weil McLain 468 boilers came with a Wayne Blue Angle burner. In the installation manual for this burner there is no specific recommendation for the Weil McLain 468 boiler, however the manufacturer of the burner recommends a 1.25 60° or 80° with a recommendation of hollow spray pattern at firing rates below 2.00 GPH. I recall having good luck with 80° hollow on the 368 boiler but I have no recommendation for the 468 boiler.
Many early model Weil McLain 468 boilers used a Wayne Combustion M series burners. Those burners were labeled as Weil McLain burners. Some of those burners were equipped with a FlameLock (flame retention head) and some without a flame retention head. Those without the flame retention head worked well with 80° hollow nozzles. The FlameLock head is able to handle the 70° and 80° spray angle nicely.
Of Course this assumes that the original oil burner has not been replaced over the years. That boiler was only manufactured between 1987 and 1995.
So when @Intplm. asked you for "What Burner?" there was a reason.
Can you provide that information?
2 -
A dumpster...toss it in there.HVACNUT said:What if it's a QB-180? What nozzle would I use then?
Did they ever put a QB-180 on of those boilers...on purpose?There was an error rendering this rich post.
2 -
It was a trick question. And you scored 100.STEVEusaPA said:What if it's a QB-180? What nozzle would I use then?
A dumpster...toss it in there. Did they ever put a QB-180 on of those boilers...on purpose?3