Hydronic Gas Boiler high pressure issue
unbelievable21
unbelievable21 Member Posts: 10
edited October 2022 in Gas Heating
I have a pennco boiler installed in 2001 in a house i just bought. Recently I replaced a few parts with new: circ pump, water feeder with backflow, 2 new zone valves and zone board, new drain at boiler inlet, new expansion tank and pressure relief valve, new auto can vent. All these new parts and I now have a high pressure issue. Ill try to explain:
Boiler is filled to 12 psi. Thermostats kick on and boiler temp rises to 180F and pressure to 20psi (normal). Thermostats shut off. Temp decreases slowly back to 120F and pressure remains at 20psi. Should drop back down to ~12. Let's say if i turn thermostats back on at this point - temp rises to 180F and psi rises a little more to 22psi. Shut off thermostats and temp decreases as usual and pressure stays at 22psi. This continues every time I turn on the thermostats - pressure keeps increasing slightly until 30psi in which pressure relief valve starts to leak out water. In other words - pressure never retreats. (Keep in mind Feeder is set at 12psi out of the box. Could it be faulty? Could it have been damaged when pressed or soldered that would make it do this?).
I tried a test in which i shut off the water to the boiler before the feeder and released some water to drop pressure back to 12 psi. I turned on both thermostats and again temp rises to 180F and pressure to 20psi. Turned off thermostats and pressure still remained at 20psi the first time. I decided this may have been due to the small amount of water between shutoff valve and feeder which held water and was most likely let in during or after this first run. So I relieved some more water again from the boiler with shutoff valve still closed and dropped the pressure back to 12psi. I turned on both thermostats again. Temp rose to 180F and pressure to 20psi. I shut off thermostats and the pressure dropped to about 10psi. I did not do anything again. About 8 hours later when I came back to it, the pressure showed closer to 5 psi.
1 other thing id like to mention is for example when the boiler installed gauge reads 20psi and shutoff water valve is open - i hook up a water gauge to drain valve and I get 12 psi on that gauge. When the boiler installed gauge reads 20psi and the shutoff valve is closed and I hook up this water gauge to the drain valves - I get 0psi on this gauge on these drain valves.
Thats the extent of my testing with this issue and I was hoping someone could give their opinion on possibilities for why this is happening etc. My opinion is it is a faulty new feeder or installation of it. But would be helpful to get some opinions before buying and installing another 1 if for some reason that it is not the case. Because my only thinking is if I am getting 2 different pressure readings in 2 different spots then maybe the feeder is working fine but is detecting a different pressure in that area . if that even makes sense. Anyways, Any help would be appreciated this has been exhausting. I can provide any more information if needed, thanks.
  • ScottSecor
    ScottSecor Member Posts: 995
    edited October 2022
    Was expansion tank set to 12psi (same as the feeder)? I'm guessing we get about one in fifteen expansion tanks that are no where near 12psi right out of the box. I would say about one in a few hundred pressure reducing valves are not set correctly or faulty.
  • unbelievable21
    Thanks for the response. I checked the new tank and did the tap test on it, doesnt sound like any water is in it. Checked pressure again now with tire gauge and 3 readings between 11-13psi (precharge is 12).
    Jamie Hall Member Posts: 26,165
    The tap test is unreliable with bladder tanks. The only reliable way to check the tank is to isolate it from the system and get all the water out of it and then adjust the air pressure to what the feed valve is set for -- 12 psi. Then hook it back up to the system, Some installations have convenient valves to do that. Most don't.
  • unbelievable21
    Ok. i do not have those convenient valves to do that so easily. based on my steps I did would that be your first guess for the issue im having? The tank and feeder are both new.
    hot_rod Member Posts: 25,324
    Set the pressure to 12 psi cold, then valve off the fill valve. Does pressure rise to 30 psi?
    is so the tank is waterlogged or diaphragm stuck against the nipple
  • unbelievable21
    when valved off it rises from 12 to 20psi when heat is turned on the first time. when done heating the temperature drops and the pressure remains at 20psi. i drain a little water from relief valve at this point and boiler gauge gets back to 12. next time i turn on heat temp rise and pressure rises again like normal. at this point when i turn off heat both the temperature and pressure go down as they should. (the reason i think it pressure remains at 20psi after valve is closed the first time heat is turned on is because in my estimation the filler , even though it is set at 12psi, allows more water in between the shutoff valve but before the filler...would that make sense that filler is faulty?)
  • neilc
    neilc Member Posts: 3,028
    where is the tank and make up feed in relation to your circulator?
    can you post a picture showing all that?
    known to beat dead horses
  • unbelievable21
    edited October 2022
    circ is at the inlet to the boiler. tank is right after the outlet from the boiler. feed is off the main water supply after the shut off valve to boiler and after the backflow w/ vent. the piping right after this feeder joins with the returns as it meets the circ at inlet of boiler. attached some pics
    Temperature effects pressure also. When you read 12 psi what is the boiler temperature?
    what is the temperature when it reads 20?
    when the boilers shuts off  pressure at 20, you would need to wait until it drops to the same temperature it was when it started at 12
    water expands and pressure goes up, pressure drops as it cools down, basically
    Read all pressures with the power off so circulators are not running
    Looks like a new press ball valve the fill. Very remote chance it is not shutting off 100%
    if it never goes above 20 psi it will work fine. That is not excessive.  If it keeps creeping above that, water is being added.
    EBEBRATT-Ed Member Posts: 18,209
    Unless I am mistaken you have the expansion tank connected to the discharge side of the circulator and the feeder connected to the suction side. The have to be connected to the same side. I would disconnect the feeder and tie it into the expansion tank pipe.
    Your gauge may be off. Install a temp pressure gauge on one of your boiler drain valves with a garden hose connector.
    Remove your expansion tank and check the pressure of the air side while it is off the boiler
    mattmia2neilc
  • EBEBRATT-ED is on the right track. It looks to me that the boiler feed is on the return from the system and the expansion tank is on the supply to the system. So when the circulator pump kicks on it feel the resistance of the water being pulled back from the system and part of the force of the water being pushed into the system is being canceled out by the expansion tank.. Normally we like to connect the water supply at the point of no pressure change, which is the expansion tank.
    I realize you didn't have a problem before you changed these components, I have seen this problem dealt with by lowering the boiler feed pressure to about 5-7 lb. When the circulator pump kicks on and goes through a few Cycles the pressure increases to the normal pressure. This wouldn't be the best solution because it lessens the efficiency of the pump and the air separator doesn't work as well. However it may be a solution until the system can be replied.
    Unless I am mistaken you have the expansion tank connected to the discharge side of the circulator and the feeder connected to the suction side. The have to be connected to the same side. I would disconnect the feeder and tie it into the expansion tank pipe. Your gauge may be off. Install a temp pressure gauge on one of your boiler drain valves with a garden hose connector. Remove your expansion tank and check the pressure of the air side while it is off the boiler
    Good catch.
     Sure be nice to get the tank and fill on that boiler return pipe. Plenty of room in the piping above the circulator. A 1 hour job with a press tool and a few fittings 🥴
    Air purger, my least favorite type, is in a good location.
    The tank does not need to be at or below the air purger .
  • unbelievable21
    the feeder is there to regulate the pressure coming from the main (at around 45 psi) to ~12psi. If i move it to where you say then wouldn't water enter the boiler unregulated at 45psi?
    gauge being off is a possibility. I have tested at the drains and received different pressure then what is indicated on tridicator. For example, when it says 20psi on boiler, i am seeing 12psi at drain by the circ.
  • unbelievable21
    water discharges from the boiler from that pipe in the first pic. it loops around and up into the air scoop/expansion tank. it is on the supply FROM the boiler. the circ is located on the supply before the boiler, as well as the feeder before joining together with the returns
  • unbelievable21
    it has gone above 20psi. that is the issue. pressure never goes down on gauge. temperature does. pressure stays at 20psi and when i run boiler again it goes to ~22psi. then i shut off and it stays there but temp drops. next time i run boiler pressure goes to ~24psi. i shut off and it stays at 24psi and temp decreases as usual. process continues until 30psi is reached and PRV starts to leak.
  • neilc
    Ed and Lyle nail it,
    this is pumping away x's 2, 1.01, fail,
    connect the feed to the tank,
    right now you're sucking from the feed as you pump to where the pressure does not change(at the tank),
    I bet(know) if you disable the boiler, and just run the circ,
    you would see the same increase, from cold fill 12, up to the 20 you're landing at,
    move the feed to the tank connection,
    and pump away,
    there's a book in the store here that explains this,
    or most boiler piping diagrams show same.
  • neilc
    the system pressure at the tank doesn't change*,
    when the circ pumps towards the tank, the inlet of the circ is a lower pressure than at that the tank,
    if your feed is before the circ, the feed sees that lower pressure, and compensates raising the pressure into the circ, to the preset 12~15,
    now on the outlet of the circ, (incorrectly pushing into the tank), that pressure rises, taking up some of the tank air cushion, and you raise the entire system pressure all the way thru the system, until the feed into the circ is back up to the preset 12~15, note that you're now seeing 20~25, or whatever, on the circ discharge side,
    and have now raised the entire static system pressure (the pressure when the circ is off) to the 20 you're seeing,
    * doesn't change unless the circ pulls on the inlet and feed as described above,
    try this, system/circ off,
    lower the system pressure to a cold 12~15,
    shut off the manual feed valve to the system fill,
    now start the circ, let it run,
    shut the circ back off and the system will be back to the 12~15 you started at,
  • pedmec
    pedmec Member Posts: 1,231
    location of point of no pressure change is exactly the problem in relation to the circulator. Circulator moves water by creating a pressure differential in the system. Where the pressure differential happens depends on the the location of the expansion tank. If you pump into the expansion tank the differential happens mostly on the suction side of the circulator. So the pressure that you are seeing depends on where the gauge is located. Picture if you can.
    System fill pressure is 12 psi @ 60 degrees (cold start)
    System calls for heat.
    Circulator comes on and (depending on size of circulator) creates the pressure differential.
    But because its pumping into boiler with expansion tank on discharge it needs to happen on the suction side. Now say for **** and giggles the circulator creates a 6 psi differential. Most of it has to happen on the suction side.
    System pressure at suction drops to 6 psi. fill valve, feeling only 6 psi starts to add water to system until it reaches 12 psi. the boiler water, which was at cold start starts to heat up and expands.
    thermostat satisfies. circulator stops and the new psi is 20.
    Because you have zone valves you also have multiple system curves so that differential is going to change with whatever zone is on.
  • neilc
    That's a great explanation @neilc , and I completely follow what you said.
    I will do that test tonight. BTW, once the system pressure is set, I leave the auto feed off.
    The million dollar question is, without reconfiguring the entire system to pumping away, is there a location that I can put the expansion tank where it can do the job that it is supposed to do?
    I leave my fill valves closed, but I check the boiler pressures periodically, next day, then 2 days, 5 days, a week, 2 weeks at the most,
    I think it's easier to move the feed connection over to the tank, but,
    you could move your tank to be on the same line as the feed also,
    your call.
  • pedmec
    In the situation you are describing, absolutely. In that case i would check the precharge on the tank, but also make sure that the temperature of the water does not continue to increase as the cast iron will, even thou there is not flame, continue to increase the water temperature in the boiler. The cast iron has good thermal mass and with no water flowing will continue transferring heat from the cast iron to the boiler water.
  • neilc
    well now, wait,
    you ran the boiler without the circ? and the pressure went up to 20, and did not come back down ?
    with out the circ you would not have heated all the system water, so the expansion wasn't even complete,
    "It's like the tank isn't even there."
    have you checked the air pressure under the tank?
    and that there's no water there? ie:failed tank?
    can you isolate the tank from the rest of the system(water pressure)?
  • neilc
    MikeAmann said:
    But my plan is to relocate the tank to a more appropriate PONPC location and install a pressure gauge at the air scoop where the tank was located.
    So without reconfiguring the entire system, I would want to move the tank to the suction side of the circulator, correct?
    yup,
    and it's the tank that is the PONPC, which you want to pump away from,
    PONPC is not a "other" location in the system, it's the tank where it connects,
    the tank connection wants to be on the suction side of the circ.
    MikeAmann
  • pedmec
    in my opinion it would be just as easy to move the circulator after the expansion tank or mve the expansion tank close to the suction side of the circulator.
    on the supply side there is a straight piece copper to cut the circulator in.
  • neilc
    Nope,
    wrong, or I'm reading this wrong.
    when you had the tank disconnected, and were blowing on it,
    YOU SHOULD HAVE PRECHARGED THE AIR IN THE TANK TO what you want for system pressure, 12~15,
    that was your opportunity,
    now it's a do over.
    precharge air in the tank first, with no water pressure on it,
    then you add water to the system,
    I don't see where the Y, or tank is connected now,
    wanna post another distant picture showing tank, and circ, and the piping between, all in one
    SuperTech
    edited October 2022
    A couple of things about expansion tanks which are relevant. First, there are two kinds -- bladder tanks and diaphragm tanks. In bladder tanks, when there is no water in them, the bladder will unfold and be lying on or near the water connection. In that condition, the air pressure on the AIR side should be the same as (not more than) the cold system pressure. The same is true of diaphragm tanks, except that there will be some air trapped on the water side -- but not much. In that condition, when the system is cold, there is a maximum of air volume in the tank. As the system warms up and the water expands, it expands into the water side, and this moves the bladder up, compressing the air. Since there is a large volume of air, and the volume of water doesn't change all that much, the pressure won't change much either.
    Also the question was asked shouldn't the tank get warm as the water flows in? Well, a little -- but note what I said above about the volume of water. It isn't much, and so the temperature change in the tank will be minimal.
    Edit -- one other thing I might add: some people have the idea that you can tap on the side of an expansion tank and get some idea as to how much water is in it. This works, sort of, with a diaphragm tank. Doesn't work with a bladder tank, as the bladder -- not the water -- is what is in contact with the wall.
    MikeAmannWMno57SuperTech
    edited October 2022
    It be highly unusual to get a bag or bladder tank like that from Home Depot, You have a diaphragm tank. The other indication is the crimp around the tank, a hoop inside holds the diaphram in place in that crimp groove
    A very simple correction would be a press tee into the horizontal tube at the circ. Remove the circ mounting bolts to allow you to press a tee into that location, move the tank and fill valve there and now you are pumping away
    Charge the tank to what you intend to fill to.
    The Amtrol Handbook available at their site has the math and charts to figure out expansion volume
    Ae have done several coffee with Caleffi webinars in expansion tank sizing. Go to the Caleffi North America you tube playlist
  • pedmec
    Just a crazy question. you have multiple air separators in your system? The new pictures don't look anything from what was previously posted.
    MikeAmann said:
    @hot_rod Would you label the supply and return in your pic?
    The return is the piping in the lower portion of this pic, So any piping connected to, and above that red circ
    So that horizontal pipe, lowest in the pic is where a tee could be installed for the tank and fill.
    Thus turns the system into a “pumping away” configuration
    You have  plenty of expansion tank capacity
    MikeAmann
    The tank needs to be at or near the inlet if the circ. If the circ was on the supply after the air purger, then the tank would be fine under the purger
    Im assuming your circ is pumping into the boiler? Should be an arrow in the body.
    Wherever the tank get mounted, so should the fill valve
    I think my proposed location would require the least amount of modification
  • SuperTech
    SuperTech Member Posts: 2,611
    @MikeAmann that green 007 shouldn't be installed motor facing up like that, it's in the installation instructions.  It could easily trap air and burn out the circulator motor. That was the craziest description of a way someone installed an expansion tank that I have ever heard. Putting the tank into a vacuum? Pre filling with water? I would drain it back down, correct the circulator installation, correctly pre charge the tank and tie in the fill valve to the expansion tank location.
    MikeAmann
  • unbelievable21
    so to recap as OP, my issue is because water regulator/feeder is before the circulator and not on the supply side before exp tank? It has been like this for 20 years and never had high pressure increases like it is now. I should move feeder with backflow to right before exp tank?
  • unbelievable21
    edited October 2022
  • pedmec
    I think that was stated multiple times in the post including by yours truly