Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

HONEYWELL S86U inernal error

Options
Paul_11
Paul_11 Member Posts: 210
I installed an S86U when I first installed a Peerless gas atmospheric boiler in 2013 & it lasted until 07/11/22. We had to replace it again on 10/04/22.

Nothing with the boiler has changed

Is this just a case of a bad S86U or could something else cause this?

I have searched this site and GOOGLE, but no one seems to have any good reasons
Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER

A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-0593

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,546
    Options
    Nothing I know of. Hopefully it's under warranty. They don't make anything like they used to
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,867
    edited October 2022
    Options
    If it happens again... then it is not the control. Look for a chaffed wire or something that may be causing overcurrent. Did your customer add a smart thermostat just before the first failure?
    Could a staple in a wire you put in 2013 finally wear thru somewhere?
    Ware and tare. or is it spelled wear a tear Oh stop crying!

    Just pulling at straws here.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2