HONEYWELL S86U inernal error

Paul_11
Paul_11 Member Posts: 210
I installed an S86U when I first installed a Peerless gas atmospheric boiler in 2013 & it lasted until 07/11/22. We had to replace it again on 10/04/22.

Nothing with the boiler has changed

Is this just a case of a bad S86U or could something else cause this?

I have searched this site and GOOGLE, but no one seems to have any good reasons
Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER

A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-0593

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    Nothing I know of. Hopefully it's under warranty. They don't make anything like they used to
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited October 2022
    If it happens again... then it is not the control. Look for a chaffed wire or something that may be causing overcurrent. Did your customer add a smart thermostat just before the first failure?
    Could a staple in a wire you put in 2013 finally wear thru somewhere?
    Ware and tare. or is it spelled wear a tear Oh stop crying!

    Just pulling at straws here.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?