EZ GAS PRO CAR9859210FRU
Bill Julian
Member Posts: 164
in Gas Heating
Installed this today but did not drill out the orifice, is it required? There is already a hole drilled out looks like 3/16. Probably 70,000 btus in whole house. HW heat. Also how to set the electrode slide. Ill called the tech line tomorrow but picking your brain here.
1. Don't just drill the hole any bigger unless you understand the pressure to orifice ratio for the BTU content of the gas you are using.
2. Don't operate the burner unless you have the proper tools to set up the burner adjustments with combustion testing equipment.
3. Did you follow the installation instruction for proper commissioning of the burner?
4. Has the heat exchanger and combustion chamber been thoroughly cleaned?
5. Is the vent connector and chimney free of any blockages
That is just in 2 minutes off the top of my head.Edward Young Retired
What make and model boiler? Carlin lists the orifice size needed in their OEM guide, for natural and LP gas and BTU input.0
CAR9859210FRU
EZGAS PRO UNIV 10 AIR TUBE0 -
Its 75-100.00BTU 3/160
Looks predrilled at 3/16 to the eye0
Boiler is W/M 4 section Gold w/tankless0
If Carlin knew what boiler it was going in, they would predrill the orifice. If not you're on your own. The manual shows the correct hole size according to the BTU needed. Use a drill bit to check the size of the factory hole.0
The WTGO-4 has 2 possible input ratings: 140,000 and 168,000 BTU per hour.
The EZ-Gas manual is here:
https://carlincombustion.com/wp-content/uploads/MNEZGas-061715-production.pdf
The lower rating calls for a 1/4" hole.
The higher calls for a 9/32" hole.
Try the lower one first. If the boiler performs well, you don't need to re-drill.All Steamed Up, Inc.
Consulting1 -
check that boiler 3 section WGTO0