Horizontal pipe in Hartford Loop
Scott216
Member Posts: 13
I just came across a great document from Peerless about one-pipe steam systems. It says that the horizontal pipe going into the Hartford loop (see picture) should be a close nipple. I just redid the piping on my boiler, and not knowing this, I used an 8" nipple. I could change this, but I thought I ask people's opinion first. I have fired up the boiler a few times since redoing the piping and there's no water hammer. Since it's still warm in NJ, the boiler has only been on for testing. Is this something that is often an issue? Anyone know why Peerless recommends a short nipple here? Their document doesn't go into the reason for this.
There's ideal, and there's works. If it doesn't bang, don't worry about it.Br. Jamie, osb
You have steam in the equalizer and cooler water coming in the Hartford Loop. When these two meet, you can have rapid condensation creating a low pressure at the equalizer. This will cause water to rush into fill the void. The slug rushing through the nipple picks up speed till it slams into the tee so the close nipple limits the noise, and impact force, of the slug. Hence their advice for mid-cycle water hammer.0
Just as a heads up, this isn’t Peerless only, every manufacturer says close nipple. This is standard practice for a steam boiler, instructions or not.
The best way is with a wye instead of a tee.0 -
A close nipple or Y is ideal. It is where steam and water meet so to minimize water hammer the shortest connection is used.
Like @Jamie Hall said if it doesn't hammer leave it alone0 -
If it was mine I sure wouldn't even think about taking it apart unless it complained.
The best engineering advice works all the time. But many things can work some of the time. They come under my heading of "If it ain't broke don't fix it!"0
If every boiler and furnace that were not installed by the book were shut down 90% of the people would freeze.0
- 50 Industry Classes