Wiring smart thermostat to two boilers
BMurrins
Member Posts: 45
Hey guys,
I'm trying to connect a Honeywell T9 thermostat to control two parallel hydronic boilers both fitted with a L8148.
Can someone please tell me how to properly wire a dpdt switch i have here (r8222d) or a RIB2421B spdt switch that i also have here, without having to worry about burning out the transformers? For some reason I cant figure this one out probably out of fear of burning them out and making an expensive mistake.
Ill attach a simple diagram i drew to show how theyre wired so far. Mind you that this diagram doesnt include the vent damper molex connection that my aquastats have. sort of irrelevant to the question im asking so i just went for the first diagram that i saw.
Boiler 2 on the left, Boiler 1 on the right
same time off the same statEBEBRATT-Ed said:Are you planning on running both boilers at the same time off the same stat? Or are you going to run 1 boiler or the other? Switch boilers manually or automatically?
You can do it with the R8222D but you will need an additional 120-24 volt transformer.
wire term 1 on the R8222d to TV on one aquastat
wire term3 to T on the same aquastat
wire term 4 to tv on the other aquastat
wire term 6 to t on that aquastat
mount new transformer and power line side 120 volt
on the 24 volt side the common goes to the coil of the R8222D and to common on the thermostat.
the 24 volt hot goes to R on the thermostat
w from the thermostat goes to the coil of the R8222D
There may be cleaner easier ways to do this but with what you have this will work
Sorry its crude. You don't need an additional transformer. The one in the aquastat is 40 va.
Out of curiosity and because I’m currently trying to figure out a solution for a two boiler system, Is your application as simple as you need both boilers to fire every time in order to satisfy demand at all times?0
hey guys thanks for the responses so far i really appreciate it.
yeah this is for both boilers to fire simultaneouslynorthlakes said:Out of curiosity and because I’m currently trying to figure out a solution for a two boiler system, Is your application as simple as you need both boilers to fire every time in order to satisfy demand at all times?
I think HVACNUT has given you the solution to firing both boilers at the same time. The question of "why" is pretty valid. When you control boilers that way you often end up with one boiler actually firing more than the other (one aquastat being a little more sensitive) and both boilers short cycling. A simple two-boiler controller will auto-rotate the boilers run times and only fire both when the load requires it.https://www.supplyhouse.com/Tekmar-261-Boiler-Control-Two-Stage-Boiler-Setpoint-4153000-p"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
it it’s not the most ideal setup that we have here but it’s a large apartment building being heated by 2 400k btu crowns. Horrible design but to modernize it, we’d be way over budget right now. Looking to get through the winter and redesign it come summer 20230
2 -
The transformer in the L8148 is rates at .8 amps @ 24 volt. More like a 20va. I don't think it's a 40 va.
The r8222d coil inrush is 20va sealed is about 10va0