Bypass with low loss header
SpicyLlama
Member Posts: 2
Would a bypass be required on a low temperature system fitted with a low loss header?
What type of bypass were you thinking? Pressure or temperature?
If the secondary side had a fixed speed circulator with 4 or more zone valves or actuators, a pressure bypass would be a good addition
Or use a delta P style circulator if zone valves are used.
Temp bypass. Only 3 zones (dhw/rads/underfloor)0
what type hat type of boiler? If it is cast iron or steel you don’t need a LLH
If it is a mod con you may not need a bypass?
Need to know more about the system componentsBob "hot rod" Rohr
If your boiler is cast iron non condensing and a low loss header was installed I would suggest it’s not a by pass you need ,what is needed would be danfoss thermic valve to prevent prolonged low temperature return temps which will possibly cause flue gas condensation and ruin your boiler . A thermic valve is the better choice then a valved by pass which will never really have a idea of what the return temp is while a thermic valve has some what of a brain . In which case a hydro separator is good for hydronic pump separation but a 4 port buffer tank like a boiler buddy would have been a better choice being it would give you some buffering and possible alleviate any short cycling by giving you volume being most radiant systems don’t have a lot of volume and after initially coming up to temp they don’t shed a lot of btu s and w a non modulating boiler short cycling usually starts ,while a buffer tank will store the extra heat and the radiant slips off it until the temp falls low enough to re engage the boiler .
Food for thought
Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
This method give you mix temperature, based on outdoor temperature, and protects the boilerBob "hot rod" Rohr