Bypass with low loss header
SpicyLlama
Member Posts: 2
Would a bypass be required on a low temperature system fitted with a low loss header?
0
Comments
-
What type of bypass were you thinking? Pressure or temperature?
If the secondary side had a fixed speed circulator with 4 or more zone valves or actuators, a pressure bypass would be a good addition
Or use a delta P style circulator if zone valves are used.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Temp bypass. Only 3 zones (dhw/rads/underfloor)0
-
what type hat type of boiler? If it is cast iron or steel you don’t need a LLH
If it is a mod con you may not need a bypass?
Need to know more about the system componentsBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If your boiler is cast iron non condensing and a low loss header was installed I would suggest it’s not a by pass you need ,what is needed would be danfoss thermic valve to prevent prolonged low temperature return temps which will possibly cause flue gas condensation and ruin your boiler . A thermic valve is the better choice then a valved by pass which will never really have a idea of what the return temp is while a thermic valve has some what of a brain . In which case a hydro separator is good for hydronic pump separation but a 4 port buffer tank like a boiler buddy would have been a better choice being it would give you some buffering and possible alleviate any short cycling by giving you volume being most radiant systems don’t have a lot of volume and after initially coming up to temp they don’t shed a lot of btu s and w a non modulating boiler short cycling usually starts ,while a buffer tank will store the extra heat and the radiant slips off it until the temp falls low enough to re engage the boiler .
Food for thought
Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
This method give you mix temperature, based on outdoor temperature, and protects the boilerBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements