Nest Thermostat Dual System
 
            
                
                    sphelps81                
                
                    Member Posts: 2                
            
                        
            
                    I have a dual transformer systems and bought a 24 volt c wire adapter since i do not have a c wire. my rh and rc terminals are in use. with the adapter can I put one of the wires with the rc wire terminal and then the other to the c. If I put the rc wire that’s already there with the adapter wire will it hurt anything? Its currently running fine that way.                
                0                
            Comments
- 
            The NEST may not care where it gets its 24VAC power from, Rc to C or Rh to C as long as it gets a constant 24VAC power. Also if you look at your HVAC equipment the individual wires to the thermostat's Rc and Rh terminals may be wired together to an R terminal there.National - U.S. Gas Boiler 45+ Years Old
 Steam 300 SQ. FT. - EDR 347
 One Pipe System0
- 
            So if I put the adapter wire from the 24volt in with the existing Rc wire it shouldn’t hurt my air unit then?0
- 
            If it were me, I would skip the Rh, and use that wire for a C, and then install a simple relay control at the cooling equipment to operate the heating system.
 Of course, I don’t know where these wires are going, so that idea may not work well. If the heating and cooling equipment is next to each other, this would be relatively simple. If you have some basic wiring skills. It’s low voltage, harmless0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements