Location of a panel radiator bleed valve

Options
skiereric
skiereric Member Posts: 66
Does it matter what side of the radiator the bleed valve is located on?

The radiators are distributed via a manifold, with separate supply and returns.

Supply bottom right. Return bottom left.

My issue is that a few rads bleed valves are too close to a wall making bleeding a bit cumbersome,



Comments

  • Alan (California Radiant) Forbes
    Options
    Bleed valves are usually located on the opposite side of the water inlet.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • pecmsg
    pecmsg Member Posts: 4,861
    Options
    Bleed valves are usually located on the opposite side of the water inlet.
    and at a high point. 
  • mattmia2
    mattmia2 Member Posts: 9,667
    Options
    But as long as it is high it doesn't matter much as long as you have good air elimination or management in the system. Once it is circulating the system should be designed to eventually get it to the boiler and vent it or put it in a compression tank.