Steam question
Snowmelt
Member Posts: 1,457
Went to a new customers house. Residential but I never as this set up.
1 pipe system 2 take off. Then the odd thing was under 5 feet of linear pipe of supply it teed back to the return. Boiler was leaking roughly 12 years old . They already have a contract for the boiler replacement with Sears so it’s a Utica boiler. I believe the pipes are three inch.
Please give me any info on this set up.
Looks like they didn't read the manual and hooked it up to the header for the old boiler. Make sure sears abates that aircell if that is what it is.0
Or is the header in that back corner with the equalizer connected after the mains tee off? It is hard to see that is going on back in that corner. If that is the case those may just be drips for the main or a section of the main that can't drain elsewhere.0
Yes counterflow , ca someone explain how that works ….. also the two vertices pipes in the front is the return. Should they go in the return separately instead of together ?0
The 45 I the back corner is actually the riser , it’s 3 inch going on a 45 then elbows to the right of the boiler. Then looks like two more elbows to two take off then reducing to 1-1/2 to the opposite side of boiler then goes down to Hartford loop.
Net question is since it’s a drip system is that why it’s 3 inch?0 -
You can’t see it but the two pipes in front going down is teed into the mains going out .0
The drips should go in to the return separately below the water line. The way it is now steam can travel from one to the other and potential do things like trap a pocket of air somewhere/close a vent that shouldn't close yet.0
That’s what I thougt. Luckily that looks like an easy fix,0
Yes, the two drips can be connected together but only below the boiler water line not above it as it is now0
are those the only 2 returns for the system?
I don't think you have the same worries with the return drips connected high there,
as long as there's good working main vents at the ends of the 2 supply mains, steam will push to the venting.
these are not steam extensions, or dry returns, where a high connection would matter.
other than the boiler leaking,
what issues are you trying to solve for there?known to beat dead horses1 -
Boiler is leaking, not my ob but I’m going to assist on a new install,it’s a Sears Customer so there installing a Carrier which is Utica ..0
Another question would be an I use both risers and make a drop header if I have the space ?0
Yes-- do. It can help a lot. Remember that you need to go high enough with the risers -- 24 inches sounds good -- but then you can come back down as low as you need to with the drop header -- just clear the top of the boiler! Also you don't need to come all that far over with the horizontal sections from the risers -- a foot is probably quite enough. Remember riser, riser, steam main(s), equalizer -- slope to equalizer. But you already knew that!Snowmelt said:Another question would be an I use both risers and make a drop header if I have the space ?
Actually it's probably "Utica Heating" which is a rebranded Dunkirk. How much do you want to bet they will want to reduce the size of the steam outlets?Snowmelt said:Boiler is leaking, not my ob but I’m going to assist on a new install,it’s a Sears Customer so there installing a Carrier which is Utica ..
Consulting0 -
It probably will work ok because it is so close to the boiler but why do it twice if it doesn't.neilc said:are those the only 2 returns for the system?