Understanding Zone Valve
zvalve
Member Posts: 83
in Gas Heating
Looks like a Honeywell. Yes, the valve stem moves very little and the valve may still be good. You can't really tell if the valve is working properly without the operator installed as the operator exerts constant pressure when closed.
Replacement operator here.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
I had one that the ball was broken inside. Still looking for half of it. It has a rubber ball the closes on the seat to stop the flow. As Alan and Zman have said try power head if that doesn't fix it replace the insides ie ball and shaft. You don't have to solder anything just release the pressure and drain, then pull those four bolts.1
Thanks everyone, replaced powerhead and the zone experienced some warming but not much hot water was flowing by so this zone valve went from causing the zone to be overheated with the old powerhead to be barely warm with the new powerhead. Hence it seems like the shaft and ball is no good inside the zone valve. Will try to rebuild it as heat head suggested0
When you open up the valve for rebuild, examine the rubber ball closely. If it is pitted badly, it is an indication that somehow oxygenated water is getting into your system. Honeywell says that this ball will deteriorate fast if oxygenated water enters the circuit constantly. So I would check to see if there are any leaks in the circuits as well which allows water to be constantly replenished through the fill valve.zvalve said:Thanks everyone, replaced powerhead and the zone experienced some warming but not much hot water was flowing by so this zone valve went from causing the zone to be overheated with the old powerhead to be barely warm with the new powerhead. Hence it seems like the shaft and ball is no good inside the zone valve. Will try to rebuild it as heat head suggested
1
- 87K THE MAIN WALL
- 112 Chimneys & Flues
- 106 Geothermal
- 980 Plumbing
- 388 Solar
