BTU and pipe diameters...
Options
rsilvers
Member Posts: 182
How big a deal is it to leave a 3 foot section of newly-installed components that are 1-1/4 size for a system that has a 1-1/2 inch boiler loop to a hydro-seperator of 1-1/2 size and is 180,000 BTU? The output of the hydro-seperator would pass through this smaller section for a few feet before branching to eight 3/4 inch zones.
My understanding is that as long as you can flow 18 GPM, things are good. I used a head-loss calculator and it says that changing the pipe size down for 3 feet raises the water velocity by 1.5 fps and has a cost of 0.15 in head loss as a result. That will make the pump work a small amount harder, but the BTUs should still flow. Am I correct? I think its only about a 300 BTU reduction for a given pump watts, and slightly more watts will restore the BTUs.
My understanding is that as long as you can flow 18 GPM, things are good. I used a head-loss calculator and it says that changing the pipe size down for 3 feet raises the water velocity by 1.5 fps and has a cost of 0.15 in head loss as a result. That will make the pump work a small amount harder, but the BTUs should still flow. Am I correct? I think its only about a 300 BTU reduction for a given pump watts, and slightly more watts will restore the BTUs.
0
Comments
-
Quite right. The BTU flow is mass only -- and since water is incompressible, the pipe size is actually not relevant to the BTUs. What is relevant in terms of size is that a smaller size will have higher velocity and hence higher head loss (and taken to an extreme, noise and erosion problems). But a short section makes no difference to speak of.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
I decided to replace it. While it is fine, it's always going to bug me to go from 1.5 to 1.25 to 1.5 again. While I am at it, I will change the stainless steel nipples to brass to reduce the chance of galvanic corrosion.0
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements