Bad Luck with Radiator Vents!!!! Which ones next?
AdmiralYoda
AdmiralYoda Member Posts: 793
I've had some bad luck with radiator vents the past 5 years or so. I had a mix of old Gorton's and Vent-Rites and the Gorton's were being finnicky so I replaced them all with Maid O' Mists. There are six total.
A few of the MoM's failed after about a year, stuck open or shut. I replaced them, and the next year the same thing happened to the other ones. Now this year a few are not shutting like they should.
The boiler is oversized and cycles on pressure but has a Vaporstat that cuts out at 14oz with a 10oz differential. No leaks, boiler water stays clean, no surging.
Any thoughts on what brand I should try next?
  • gerry gill
    gerry gill Member Posts: 3,084
    We have had the same issues in the field and have switch to the tried and true Hoffman 40’s and Hoffman 1A’s.
    gwgillplumbingandheating.com
  • AdmiralYoda
    Any benefits of one over the other aside from the 1A being adjustable?
  • dopey27177
    dopey27177 Member Posts: 916
    Unfortunatley experimenting with the Hoffman vent valves is very expensive.
    If you use the 40s throughout the house and have a bit of a problem with how fast the steam reaches the radiator you can buy one 1a to try to balance the heat.
    Jake
  • AdmiralYoda
    @dopey27177 Thankfully I only have 6 radiators so it won't hurt that too much. My plan is to replace the vents a couple at a time with 1A's. I like having the ability to adjust the vents to balance everything as best I can (and its fun).
  • ChrisJ
    ChrisJ Member Posts: 17,346
    Have they fixed the adjusting cap design at all on the 1As?
    I thought it was amazing it could vent the same at every number depending on how the cap was sitting.