GV 90 Boiler calling all zones
Bill Julian
Member Posts: 164
in Gas Heating
I installed a GV 90 with 5 HW zone on circs. Used flow checks and what is happening is no matter what zone calls all he zone get hot. I've never seen this in all my days.
Everything is wire correctly and no zones are calling (except the one) but all feeds and returns are getting hot along with the baseboard. I can't figure it. I'm ready to just install zone valves but I'd like to know what is going on anyway. How can all zones get hot when only one (anyone) calls?
Got a pic of the flow checks?
I’ve had several hydronic service guys tell me the plastic checks in the circulators can fail in 3-5 years. If so, any one circ could induce flow in other circs.
The white colored checks are rated at 150F continuous, the black are 189F or higher.
If you have weighted checks, it’s rare, but possible for multiple ones to fail, or stick partially open.
Weighted swing checks, not a great check for Hydronics, they need a delta P to sealBob "hot rod" Rohr
How is it piped? Sounds like a particularly evil case of ghost flow or a subtle piping error.Br. Jamie, osb
Thanks for all the replies here are a few pictures Flow checks in ceiling not shown.
Also I have installed the plastic circ flow checks in circs so I have double flow checks and still have flow to all zones when ONLY ONE zone calls. We have to shut system down up strs its too hot. Confused on this one!0
The flow checks above the boiler are taco swet checks 2190
Can we get a better pix further back and w/ better lighting? makes me wonder about piping....is it piped with a boiler loop and a system loop? AKA... Primary/ secondary.
Hi Ya the 219 cardboard is removed, of course. The reason the flow checks are in the circs is b/c I did not removed them after having installed the 219's on the supply. Just didn't bother to remove them yet until I know what is causing this issue. No I did not pipe typically using system loop the boiler has its own loop internally. I have piped this way many time with no issues. I think however what I might do is pump away. Install circs on the supply.0
What might be happening is any circ that is "On" is pumping the rest of the zones as well for some unknown reason it must be a piping issue. Thanks for helping me get there with your insights.0
Does that boiler have a circ built inside of it?Bob "hot rod" Rohr
Yes it does0
the internal circ is flowing to all. You need to install 2 closely spaced tees. That will fix itTom
Montpelier Vt0 -
like this
Tom
Montpelier Vt0 -
I thought of that. What about moving the circs to the supply?0
it won't help. the internal pump will push right through them. You could swap the pumps for zone valves (if you are sure your boilers internal pump can handle the head of the system), or do the two closely spaced tees. I would suggest the tees it fixes everything. If I was doing it, I would put the pumps on the supply as well. Just simpler and ensures you are pumping away from the expansion tank.
Tom
Montpelier Vt0 -
Its a GV90-5. There is not much BB. Zone 1 26' CI BB, Zone 2 10' CI BB, Zone 3 8' CI BB, Zone 4 small space heater (tiny), Zone 5 30' Cop BB. Its a restaurant. BTU's I'm figuring the 44 feet of CI BB @ 25-28,000 BTUs and so the entire heating is probably under 50,000. So the load is certainly not excessive. Ya I think I will install the TEES. and maybe move the circs.0
Ok. Seems reasonable. I looked at it a little and thought if it was me I would pull that first 90 off the supply and put a tee there vertically. Then a short nipple below it and the other tee aiming the branch toward the lower return on the boiler, and pipe that boiler return to the branch. Then off the top and the bottom of the tees I pipe to the corresponding manifolds, in fact if the direction of flow doesn't matter to your system, flip the pumps in place and pipe to the new supply and return manifolds.Tom
Montpelier Vt1 -
Sounds right. Didn't know the internal pumps would cause so an issue I mean Ive done these before without an issue but as I recall I used the spaced Tees but not always...strange. The book also calls for 11/4, I used 1" supply and return but have such little btus??? Thanks for the help much appreciated0
O If you have to time send me a sketch of what you mean with the words you sent....if you can, if not I'll figure it anyway.0
I repiped today seems to function normally with the TEES.0
- 87.1K THE MAIN WALL
- 117 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 55 Water Quality