Taco SR504-4 Single Thermostat Wiring

Chieffy
Member Posts: 2
in Gas Heating
I have a SR504-4 Taco switching relay hooked up to 3 Aquapump circulator pumps. I would like to have 1 thermostat activate the first and second zone circulators so that both pumps turn on when the single thermostat calls for heat. Is there a way to wire this in the Taco box?
0
Comments
-
So you have 2 thermostats? Let's say Taco 1 & 2 positions on the board you want to control with one thermostat. I have not done this, but I would connect the thermostat to the R & W connections on the Taco board and jump from there to the Taco #2 position R & W with a jumper. Keep in mind that the jumper goes from R to R and a jumper goes from W to W. Don't go from R in the first position to W in the second position.
What kind of thermostat do you plan on using?0 -
@Chieffy Wire the one zone as you would normally R-R and W-W. Then the second zone just "jump" the W from the first to the W on the second. If you have any questions please give us a call here at Taco 401-942-8000 ask for Tech Support. We are here Mon-Fri 8am-5pm EST.2
-
-
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 110 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 106 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 978 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 45 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements