Old time oil burner
Yesterday
Yesterday Member Posts: 8
edited March 2022 in Oil Heating
I need to rebuild or replace an oil burner motor ( Ohio Electric MFG Co) model 985X4260AS. Any old inventory out there? How about replacing the burner unit. I see Beckett has some issues with their products. What are the possibilities? This one needs a spin to start but will continue to run. It doesn't have an external start capacitor.
«1
    Steamhead Member Posts: 17,886
    edited January 2022
    What model burner is this motor installed on? What model boiler is the burner installed in? Post some pictures of both, please.
    Nothing wrong with Beckett burners- there are millions out there and when installed and set up properly they're fine.
    Consulting
    MaxMercyYesterday
    EBEBRATT-Ed Member Posts: 18,221
    Probably a bad centrifugal switch in it. Motor shop could probably get it going but is it worth it? Probably not
    EdTheHeaterMan Member Posts: 10,765
    edited January 2022
    Are you looking to get a heater working, or is this a museum piece?
    if you just want a heater to operate, then replace the oil burner.  Beckett AFG is about the most stupid-proof burner available.  But you should have a professional technician set it up with combustion test instruments
    that model of motor looks like the Arco piggyback oil burner motor.  You needed a special short shaft fuel pump to mount on that motor. The other side of the motor had a shaft to mount the burner fan.
    MaxMercy
    I just read your response to my private message. It appears that you have a furnace. Upgrading from that old burner to a more efficient "higher flame temperature" oil burner will be a real problem. The metal in that old furnace heat exchanger has a "memory" It expands and contracts as the flame cycles on and off. It has been doing that for many years. When you introduce a more efficient Beckett AFG burner, you will cause the metal to expand and contract at a different rate. This new rate will not be in the metals "memory". This new hotter flame will cause a catastrophic heat exchanger failure within a month of the replacement burner.
    DO NOT PUT A HIGH EFFICIENCY BURNER IN THAT OLD HEATER
    Your best bet is to find the motor or find someone that has an antique oil burner with a 1725 RPM motor without a Flame Retention burner head. Ask me how I know!
    MaxMercyYesterday
    @EdTheHeaterMan , not doubting your experience, but wouldn't a down-fired flame-retention burner work in this application, since it would release the same amount of heat into the firing zone? For example, I've read and experienced that when upgrading to flame retention, one should drop the firing rate by 15 percent or so and the new burner would still produce the same amount of heat. So, if the old-style burner fired 1.00 GPH, the flame-retention upgrade burner should fire 0.85 for the same heat output. Assuming the flame was contained in a proper firebox, would that still affect the "memory?
    Consulting
    Yesterday
  • Yesterday
    Here are some pictures of the burner assembly before and after breaking them apart.
    Good one! Another trick for our collective magic bag.
    Consulting
    mattmia2 Member Posts: 13,456
    I believe that's the burner the original furnace on my parent's house that was built in 1957 had. The furnace was a luxaire lowboy. It had a different oil pump on it.
    Purely out of my curiosity, can you take a good picture of the red ratings plate for the burner?
    I think ABC made a burner like that and there were some others, Beckett Comadore and there was another one but it's slipping my mind.
    The one above might be the ABC looks farmalier.
    Yesterday
    edited January 2022
    Whatever that is, I'm pretty sure that is what my parents had. i seem to remember the red ratings plate and maybe even the motor reset button. i remember the cornders bolted to the plate on the front of the furnace and being sort of stood off, and the black hammertone plate. looking at commodore pictures it was similar but not quite the same. i think i even remember that junction box in the casting for the motor.
    I even remember the oil cups with the little spring loaded cap on them.
    @Steamhead The flame temperature will still be different. The old metal will expand and contract at a different rate. There will be a heat exchanger failure before the end of the heating season.
    Yesterday
    I agree about the new furnace but having the motor fixed at a motor shop wold get him through the winter
    CLambMikeAmannmattmia2Yesterday
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,574
    HVACNUT said:
    The bottom line is the OP needs a new furnace. Let's try to crawl out of the Stone Age.
    It's not like it hasn't been years in the making.
    Years? Decades! :)
    STEVEusaPASootBoy
    Of course everyone knows what they would do in @Yesterday situation.  But do you all know ALL the facts?
    What would you do if you were going to install a new gas furnace as soon as the main is extended to your property and that won’t be for 3 to 6 years?
    What would you do if you can’t afford a new furnace?
    what would you do if you were selling in 3 years?
    what would you do if the home was being demolished in 3 years for a new home to be built. But you don’t have anyplace to live until the construction starts in 3 years?
    I’m sure everyone here would purchase the most state of the art high efficiency oil furnace from the highest priced contractor for $$$$$$$.00 in leu of a simple motor repair and replace it yourself.
    It’s all about the new equipment when something old is broken.
    It always happens.   Whenever you commit to a plan of action for a 5 year plan, some old pieces of equipment fails and you end up spending money to replace something you are going to discard in the next few years anyway
    I'm not sure what I might do but I wouldn’t put a flame retention burner in that old furnace. I’d try to get a motor repair
    Yesterday
    HVACNUT Member Posts: 6,856
    I would've pondered all that when the clock struck 2000 AD at minimum.
    If the OP wants to keep it and service it himself, that's fine, but don't expect a modern tech to touch it when there's a lot more calls up on the board and you're in over your head before you even touch it.
    I've never actually seen that before so I probably would've done a 180 on the spot and got the hell out of Dodge right quick. No charge of course, and maybe some free advice.
    SuperTechEdTheHeaterMan
    They are no different that any old low speed burner, The unfortunate arraingment is the oil pump mounting,
    Many of those old motors has a switch inside and that is what would go bad. Even in 73 when I started we would have some of the special motors rebuilt to keep some old burners running
    Oil was $.25/gallon when i started no one would spend money for a new burner
    We had Petro burners with a step in the shaft and you couldn't buy them any more so we always has 2-3 of those rebuilt motors on the shelf
    EdTheHeaterManYesterday
    I wonder where this is located, if it was a regional product. My parents lived in southeast michigan. The ratings plate on the furnace says the make is "ocu".
    @MikeAmann, The advice is for Furnace only. Boilers can absorb the additional heat because there is water on the other side of the metal. The water won't let the metal go above 225°. The metal on a furnace heat exchanger will get well above 300° and the hotter the flame, the hotter the metal. The metal memory of the furnace heat exchanger after 40, 50 or, 75 years will be compromised in this case. Every old heat exchanger on a furnace is subject to this problem.
    It happened 2 times by my hand. One was the second year I was working on oil burners. I installed a "Delavan Head" (an aftermarket flame retention head added on a old school burner) on a neighbor's furnace. The amount of fuel used was reduced by about 18% but the heat exchanger failed within 2 months. A new furnace needed to be installed in the coldest part of the winter. So, at age 19, did I do a good job?
    The second was a mobile home furnace that was 8 years old. It was burning #2 fuel oil. The oil tank failed and the trailer park had just had new gas lines run. The homeowner wanted to convert the miller CMF80 with the manufacturer's recommended gas burner. I mentioned the problem to the customer, told them of the risk, and they elected the burner only (at about 1/2 the cost). The gas flame was actually cooler than the oil flame. The heat exchanger failed in the second season.. Back then the heat exchanger warranty was only 10 years on mobile furnaces. I installed the replacement furnace at a discount and took the 2 year old burner for another customer in the future. There were a lot of customers with limited income in my service area.
    @EdTheHeaterMan
    I here what your saying but those HXs could have been on the way out anyhow. Especially the Miller those have a poor record.
    @EBEBRATT-Ed, There are some Miller's that have lasted over 40 years. The home is in worse shape than the heater in many cases. I never change fuels on MHF from oil to gas unless the HX is less than 5 years old. That was my own personal rule. "Let the competitor deal with the problem job"
    @EdTheHeaterMan
    I changed a Miller that had a bad HX. Put a new one in and she kept complaining about an oil smell. Couldn't find anything wrong.
    We finally disconnected the furnace and pulled it out in the driveway and found a 1/4" inch hole at the end of a weld they missed at the factory.
    I don't remember if they gave us a new HX or an entire new furnace but it was ok after that. But I was done with Millers & trailers
    edited January 2022
    @EBEBRATT-Ed ... Someone needs to work on them. Sorry you had a bad experience. Knowing Miller, they probably gave you a heat exchanger. That experience would definitely turn me off Trailers early on in my career. There were so many oil furnaces in trailers and the oil dealers that depended on me sold oil to trailer folks.
    You were lucky to be able to make that choice. I had to deal with some real "Trailer Trash" back in the day.
    MikeAmann
    @MikeAmann
    I strongly recommend upgrading a boiler from the older style (pre 1970) standard burner to the higher temperature flame of a Beckett, Riello, Carlin, or any other Flame Retention head flame burner. I started my first business in the mid 1970s based on my ability to save customers big bucks by replacing old standard burners with Carlin 99CRD and & 100CRD oil burners.
    I remember saving one customer over 65% on the oil usage. It was an old movie theater that was converted to a catering hall. Low budget outfit... The floor was still on a 2-12 pitch towards the Stage/Screen side of the room (...Don't fill the wine glasses to much... LOL).
    There was an old coal steamer in the basement. Took 8 hours to get the 7.00GPH oil burner to make enough steam to satisfy the thermostat. The pressure never reached 1.5 PSI. After redesigning the fire door to accept the new Carlin 301CRD burner (moving the flame from the old ash pit combustion chamber location to the upper fire door location put the flame where the coal fire was designed). The boiler went off by pressure (1.5 PSI) within 18 minutes and the thermostat was satisfied within the hour.
    The customer was not convinced that the system would work so well. He only half trusted me, so he started the burner 4 hours before the next event after the burner job. He was pleasantly surprised when the room was heated in 1 hour. By the way... I fired the new burner at 4.50 GPH to keep the stack temperature below 500°NET.
    Do the Math. 8 Hrs x 7.00GPH = 56 gallons to get the room to temperature.
    Do the Math. 1 Hr x 4.50 GPH = Less that 4.5 Gallons because the burner did cycle on pressure.
    I think he saved enough on fuel to get the floor leveled the next year. (Not really sure on that)
    mattmia2MikeAmann
    So did the oil truck arrive with the guests at each event?
    @MikeAmann
    I think that's the most dramatic fuel-savings story we've seen here. Good job!
    Consulting
  • FStephenMasek
    FStephenMasek Member Posts: 88
    Why not just repair the motor? Maybe just a broken spring?
    Author of Illustrated Practical Asbestos: For Consultants, Contractors, Property Managers & Regulators
    I was surprised myself when the boiler made steam so fast.  At the time I knew very little about steam.  I just found out the numbers after I returned a week later (after the first wedding reception post burner job) to collect the final payment upon completion.  I still laugh about the incline floor catering hall.
    Can i see the ratings plate on the oil burner itself? I just want to know what this thing is because my parents had one. Thanks.
  • Yesterday
    edited March 2022
    "Necessity is the mother of invention..." Desperation is the father of "Get-R-Done"
    Good story.
    YesterdayMikeAmann
  • MaxMercy
    MaxMercy Member Posts: 546
    It only needs to last a month, so no big deal, but I would have soldered the points to the bar. The actual contacts are made to work this way, but the copper will eventually arc where it's crimped around the bar.
    You mentioned a new furnace on order, what kind are you putting in?
    Yesterday
  • Yesterday
  • Yesterday
    I'm told it's manufactured for Armstrong. Probably made overseas and shipped to the States.
    My wife would've told me where I can stick the motor and filed for divorce.
    What exactly are you doing with the propane at the fireplace?
    So it isn't a centrifugal switch but a potential relay? Supco makes lots of replacements both of the electromechanical and thermistor variety.
    @Yesterday, can i see that red ratings plate on the burner?