Steam radiator Frankenstein
jmet
Member Posts: 15
Can you post some pictures of the other radiators? How are they set up? Where does that return go? It is possible to have 2 pipe steam without a trap if you have a metering valve or an orifice plate and control the pressure so that only the amount of steam that the radiator can condense enters the radiator.
Before full two pipe systems with traps etc. were developed, there were two pipe steam systems which were set up in much the way you have pictured. Are there any other radiators set up that way in the building? If the building -- or even this one radiator -- is set up that way, and it works, there's no need two change anything. Systems of this type are described in "The Lost Art of Steam Heating", available from this site.Br. Jamie, osb
Connecting a drip to a one-pipe radiator, for whatever reason, doesn't make it two-pipe. Two-pipe systems allow the air to escape through the second pipe. If that's just a drip to allow the condensate to flow out without interfering with the incoming steam, it should go straight to the wet return and should never see significant steam. It it's neither, it's a problem. Either way, you need a vent to let the air out, but it should be much lower than it is now.Just another DIYer | King of Prussia, PA
Hap_Hazzard said:Connecting a drip to a one-pipe radiator, for whatever reason, doesn't make it two-pipe. Two-pipe systems allow the air to escape through the second pipe. If that's just a drip to allow the condensate to flow out without interfering with the incoming steam, it should go straight to the wet return and should never see significant steam. It it's neither, it's a problem. Either way, you need a vent to let the air out, but it should be much lower than it is now.0
Maybe slowing down the radiator venting will help. When air or steam passes over water, it causes waves to form. The faster the flow, the higher the waves. When a wave peak reaches the top of the pipe, it forms a slug, which then gets hurled against the end of the pipe with great force. This type of steam hammer is called differential shock. It can be very destructive.
https://www.youtube.com/watch?v=JyvoN1hIqRo
mattmia2 said:Can you post some pictures of the other radiators? How are they set up? Where does that return go? It is possible to have 2 pipe steam without a trap if you have a metering valve or an orifice plate and control the pressure so that only the amount of steam that the radiator can condense enters the radiator.0
just noticed the radiator lines that are pitching back to the main line seem to be slightly lower than the headers. Does this piping seem right? I would think all returns go to the hartford loop. Only one radiator is piped to the return. All others to the main.
Also.. check that main line vent situation 😂0
That particular radiator should probably be pitched toward the return. Steam shouldn't really be able to get in to that return as long as is goes in to a wet return and the water line is high enough above the return so that the steam can't push the water out of the return. Lower pressure at the boiler is better. If the boiler was replaced and the water level is now lower than that drip was designed for you will have a problem.0
The runouts have to pitch back to the main so that in the case of the one pipe radiators the condensate from the radiators can run back to the main and in the case of the 2 pipe radiator any condensation in the runout itself can run back to the main.0