New Boiler Sizing
Member Posts: 4,450
I'm replacing a 80,000 BTU Viessmann cast iron boiler that sooted up in a 1,200 square foot house which is built slab-on-grade, flat roof, single-glazed windows with very little wall insulation; one thermostat; six loops of 1/2" copper. It's a copy-cat Eichler.
I sorely want to install a Lochinvar KHB055 which has a heating capacity of 51,000 BTU and a AHRI rating of 44,000 BTU (less 15% for a piping and pickup factor). The heat loss calc's. come in at 50,000 BTU and I feel pretty good about my numbers.
The next size up boiler is a KHB085, but my supplier is out of stock and doesn't expect any for another month. I can't go with a wall-mounted boiler because it's an alcove installation and the on-demand water heater sits directly above along with other reasons. It's a very small space and the floor mounting is ideal.
What would you do?
What would you do?
heat loss calculations always have some guesstimating. And the home owners life style plas a part as @BC_20 mentioned. Seems a little risky.
Can you clean the old boiler and get it running while you wait for a larger boiler?0 -
How about a wall mount boiler (are they available) on a free standing strut rack? I have done that and it works fine0
The wiggle room in the load calc should cover it.
Upgrades to the shell will save them money and lower the load alsoBob "hot rod" Rohr
If it were my own, I'd go with the 085. I'd want the peace of mind knowing those extra BTU's are there if I need them. It's not as if its grossly oversized, especially since it modulates.
The boiler might be a big bite out of the budget and air sealing might be an expense that can't be done at the same time.
If they're monetarily blessed and can do both at the same time, then I'd go with the 055.
What's the max SWT and turn down ratio on these boilers?
42 btu/ sq ft load? Those floors must run smoking hot on design day? Or is there some supplemental heat? Typically mid to high 20s is doable from a bare slab.
Any input from the owner how much that boiler runs on cold days? If it cycles off, it’s oversized and the smaller Loch should put out what that floor can emit?Bob "hot rod" Rohr
How much gas did the existing boiler use per year? I suspect 51,000 is 2x too big.0
@Alan (California Radiant) Forbes
True. Useless to put in a boiler larger that the radiation can output.1 -
I just installed a 55 Lochinvar knight wall mount in my shop. It came with top and bottom connections , and top vent, so it would fit in that space
The floor mount you mentioned us 16” wide, 0 clearance on the right side, 24 on the left for piping access, I think the vent is out the back. A strut rack would hold it up and give you mounting for piping and pump. Check the pump spec it comes with, possibly a direct connection to the loops if they are one manifold without zone valvesBob "hot rod" Rohr
@hot_rod There's a shelf about 18" above the boiler with an on-demand against the wall. I should have sold them a combi.Did that CI boiler suffer from lack of combustion air?Choose your poison: lack of combustion air, short cycling, condensing or a combination of two or three. It was installed before we got smarter about these things.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Yes, a job like that cries out for a combi. You’ll work it out with what is available.
Headed you way for some Pace training, talking about electrification of hydronics . I’ll split the day with Nico from Thermo 2000, talking about their offerings and the AltSource tank that may skirt around Title 24Bob "hot rod" Rohr
Finished! Satisfying to get the job done, but I will never again do an alcove install.
nice! 100 lbs potatoes in a 50 lb sackBob "hot rod" Rohr
Maybe 200lb in a 50 pound sack.
Very tedious and slow, very difficult to make progress.
It's one of those job where you get up off you knees after working all day and wonder why it took so long0 -
It took half a day and 7 hole saws just to drill two holes in the roof for the vent and air. Three inches of foam, two previous tar and gravel roofs, multiple layers of plywood and surprisingly, a 12 gauge layer of copper.
That's what I like about our work. Although not always a pleasant task, the work is always different and never boring.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Finished! Satisfying to get the job done, but I will never again do an alcove install.0