Combustion analysis at high altitude
Options
CBRob
Member Posts: 291
Im trying out my first combustion gas analyzer.
Im at 9000 ft elevation and testing new install of triangle tube boiler.
I can adjust the altitude setting on the boiler but keep getting O2 levels higher than target and co2 level lower than target.
Im not going to start tweaking the boiler or anything, but wonder why my numbers are not in range.
Im at 9000 ft elevation and testing new install of triangle tube boiler.
I can adjust the altitude setting on the boiler but keep getting O2 levels higher than target and co2 level lower than target.
Im not going to start tweaking the boiler or anything, but wonder why my numbers are not in range.
0
Comments
-

0 -
The analyzer only measures O2, CO, and temp. So ignore the rest, it is just calculated by the analyzer.
I am guessing you are on Natural Gas?
The gas company derates the Natural Gas at altitude so atmospheric appliances will run more efficiently. Your boiler has a power burner of sorts and is partially compensating for the lack of air density.
A Triangle Tube, at altitude, on Natural Gas, typically needs to be "Fattened Up" (made richer) quite a bit."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
-
Very interesting... what about with propane?
I would guess most homeowners would not think to ask about the specific gravity of the fuel they're buying... but based on that table there's a roughly 30% variation in btus depending on location.Zman said:The analyzer only measures O2, CO, and temp. So ignore the rest, it is just calculated by the analyzer.
I am guessing you are on Natural Gas?
The gas company derates the Natural Gas at altitude so atmospheric appliances will run more efficiently. Your boiler has a power burner of sorts and is partially compensating for the lack of air density.
A Triangle Tube, at altitude, on Natural Gas, typically needs to be "Fattened Up" (made richer) quite a bit.1 -
-
We have to dail the O2 level to about 4.8 % at 9000 to 10.000 feet..
Greatings from Summit County.0 -
Great information you guys, appreciate the feedback.
Yep, im working with nat gas.
Zman, how do they derate methane?
Add an inert gas? Is it the ethane or propane that is added?0 -
I am not sure what they add."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 62 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements