How to build a steam heat system - Order of operations
@stormbytes
1.heat loss & type of system (one or two pipe)
2. select a & locate radiation
3. select boiler size & locate (clearance from combustables)
4. make piping layout (steam mains,dry return, wet return, heights required above the water line) size of mains and runouts. Allowance for proper pitch
5. size piping & main vents. Size runouts first, then mains then drips and then returns
6. Combustion air requirements
7. flue pipe and chimney/liner
8. electrical & controls
9. Fuel and burner piping
10. City water MU with backflow and feeder if used
11.Fill, start, test, adjust and skim
12.pipe insulation
13. permit and inspections
Since you have wet returns going in I would make provisions to drip any second floor risers into the wet returns.
If one pipe make steam take offs with a 45 (no 90s).
Are you using cast iron radiators, convectors or something else?Just another DIYer | King of Prussia, PA
So you do the permit after the work is done too?
@EBEBRATT-Ed
Its a 1-pipe system. Could you elaborate on what you mean by 'heat loss' ?EBEBRATT-Ed said:1.heat loss & type of system (one or two pipe
I presume you mean location and size of the radiators. There have been all sorts of changes to the system over the years. Radiators were added. Walls relocated. Rooms are over/under heated. I am actively planning this.EBEBRATT-Ed said:2. select a & locate radiation
No issues here. Boiler is situated at the rear of a gutted basement. Everything is wide open. No combustibles anywhere near the site.EBEBRATT-Ed said:3. select boiler size & locate (clearance from combustibles)
Runouts = take offs? (eg. smaller, horizontal/pitched pipes leading to radiators)EBEBRATT-Ed said:4. make piping layout (steam mains,dry return, wet return, heights required above the water line) size of mains and runouts. Allowance for proper pitch
What are 'drips' ?EBEBRATT-Ed said:5. size piping & main vents. Size runouts first, then mains then drips and then returns
Why are you sizing run outs first?
What is the correct way to size 2 mains?
Do you mean that second floor risers should drip condensate into their own lines tying into the wet return? I want to make sure I understand what you mean by 'second floor risers'. As the system is now, each takeoff leads to an individual radiator. There are no 'risers' per say that feed the 2nd floor (and subsequently branch out to feed radiators locally).EBEBRATT-Ed said:Since you have wet returns going in I would make provisions to drip any second floor risers into the wet returns.
Its a 1-pipe so I'll be using 45's for the take offs along with swing joints.EBEBRATT-Ed said:If one pipe make steam take offs with a 45 (no 90s).
Bit of everything. I understand 'convectors' to mean boxy looking cast iron radiators (Burnham made some way back in the day) that have no visible sections or columns. I've got a few of those, and some regular column type radiators. Will also be using cast iron baseboard radiators for the hot water loop in the basement.Hap_Hazzard said:Are you using cast iron radiators, convectors or something else?
Heat loss of house & rooms. How will you know what size radiator or boiler to install without it?
You need to read Dan's book and see my responce to your other post
- 117 Geothermal