Burnham Sunrad Radiator
stormbytes
Member Posts: 36
Do these rads need to be installed inside a wall? I'm gonna be moving a lot of things around. Wondering if I could install these freestanding beneath a window sill.
So do these radiators produce MORE heat when recessed inside a wall? Or do they need more steam/btu to heat them?EBEBRATT-Ed said:Either free standing or in a wall is fine. If recessed increase the size by 10%
@stormbytes
It's in Burnhams brochure to add 10% if recessed.
If you have a room that has a heat loss of 15000 btus and you recess the radiation you would have to select the radiation off the chart at 15000 x 1.10 =165000 -
It would be wiser to not completely recess them in outside walls and if so be sure to have some insulation between them and the outside other wise you may have issues w air vents whistling due to vacuumed forming as the system cools down . Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
That's an excellent point. Thank you!clammy said:It would be wiser to not completely recess them in outside walls and if so be sure to have some insulation between them and the outside other wise you may have issues w air vents whistling due to vacuumed forming as the system cools down . Peace and good luck clammy
I don't like the idea of recessed rads anyways. Will be pulling them out of the wall space and relocating. The steam job in this house is atrocious! It does work, but this place takes the award for shoddy workmanship.0