ADP hydronic air handler blowing cold….sometimes
mindym
Member Posts: 10
Hi - homeowner here. We have an ADP hydronic air handler installed horizontally in the attic space with a Lochinvar instant heat boiler and hot water system installed in the basement. The ADP air handler is model BSA9230D3WMOR30267. The air handler randomly blows cold. This has been going on for 3 years since we had the attic insulated and the Lochinvar installed. Prior to the those events, it worked perfectly.
Thing is, I can take my shoe and beat on the outside panel nearest the hot water inlet pipe and the hot water will start circulating. I’ve called technicians and they say they need to wait for whatever is causing it to fail completely before they can do anything. More info - until this month, it would blow cold if the outside temp got above ~50° and then dropped overnight. Now, there is no pattern for when it stops. Does anyone have any ideas as to what might be causing this?
Does this attic space get below freezing?
Is there glycol in the boiler?0 -
The attic is heated and cooled. It is mostly finished.
No glycol in the boiler.0 -
Can it go below freezing?0
Our outside temp does go below freezing but it does not affect the randomness of the needing to beat the air handler. The air handler is in an insulated, climate controlled place in the attic. Until the last month, when the outside temp was colder, the unit performed correctly.0
OK My point is If or When you lose power, a pump fails, something goes wrong you chance freezing and bursting that coil.
As far as your problem it just sounds like there an air pocket that's stopping flow. If that happens during freezing weather, then you could freeze the coil.
You need to have that line purged properly.
I Highly recommend glycol for any unit that can be exposed to freezing conditions like attics.1 -
I’ve wondered about an air bubble and the installers not properly purging the system. I have tried banging on that pipe instead of the air handler but it never got the water to circulate. There is a hose bib on the pipe going into the air handler. Would I purge it there or the one nearest the boiler?
I only stumbled upon the banging “fix” a couple years ago when I was so mad, I kicked it, and it started working. I’ve tried different areas on the outside panel but it only works in a specific area. We now call it the “kick it Charlie Brown!” method.0 -
Re losing power - we have a whole house generator so we never lose power for more than 30 seconds before it kicks in. The air handler for the 1st floor is located in the finished basement and (fingers crossed) works perfectly. Honestly, at this point we would replace the mis-functioning air handler but it is behind a knee wall the previous owners built. Given the air handler’s size, I’m pretty sure I will have to take part of the wall out for it to be replaced which would be a giant PITA
Thank you for trying to help!0 -
@mindym
Beating the poor thing will only cause damage. It could be air, it could be a sticking zone valve etc.
You know what you need? A technician with a brain. When something doesn't work it can only be a few simple things.
If they show up and go DUH they will never find the problem unless they LOOK for the problem.
And replacing the air handler is not a good idea.
How would you like to go through the nightmare of replacing it and then end up with the same problem?
Post some pictures so we can see what is going on. Pictures of the ahu and the boiler0 -
Agreed about the technician with a brain. If you know of one in the Boston area, let me know. They are in short supply or at least the places I’ve called. Pics below in a few minutes.EBEBRATT-Ed said:@mindym
The green outline on the air handler is the area you have hit to get the water to circulate. I understand banging on it is not ideal and as you can see, it has no damage after 3 years of banging.0 -
Is the coil not getting hot or is the blower not coming on when it does get hot? It looks like there is a snap disc thermostat right where you whack it. Perhaps that is sticking.0
The hot water doesn’t circulate. The blower starts blowing as soon as the thermostat calls for heat.mattmia2 said:Is the coil not getting hot or is the blower not coming on when it does get hot? It looks like there is a snap disc thermostat right where you whack it. Perhaps that is sticking.
I don't see a zone valve so I guess it has a dedicated circulator.
I agree about the sequencer but the op mentioned the fan starting as soon as the stat calls but no water circulation. Says it blows cold air so it's the circ pump not starting
It's not air bound because it works when everything starts
I could be wrong but I am not seeing anything in the AHU that will prevent the circ from starting
I looked up and read the manual and you can buy this ahu with a multitude of options so it's impossible to figure out the wiring from here
So the question is Is their something in the AHU preventing the circ pump from coming on.
Your tech needs to figure out how the circ pump starts and troubleshoot that circuit
If the stat wires go to the AHU then their must be stat wires running to the basement to start the circ pump. That's what needs to be looked at
@mindym1 -
Woke this morning to it blowing cold air. Took the panel off and held the panel switch down. Waited until blower motor was running and verified no hot water circulating. Gently (very gently 😀) tapped the relay sequencer twice with an insulated screwdriver and viola, hot water started circulating. I ordered a new one and it should be here tomorrow. Will post again after I install it.
Thank you all for your help!0 -
That's more than likely the cause, but make sure there's full 24v to the sequencer coil and secure connections. Less than 24v might not be enough to close the contacts.mindym said:Woke this morning to it blowing cold air. Took the panel off and held the panel switch down. Waited until blower motor was running and verified no hot water circulating. Gently (very gently 😀) tapped the relay sequencer twice with an insulated screwdriver and viola, hot water started circulating. I ordered a new one and it should be here tomorrow. Will post again after I install it. Thank you all for your help!1 -
@mindym
You did better that some HVAC techs who can't see a problem unless it smacks them in the face.2 -
- 15.8K Strictly Steam