Can I bypass TACO ZVC406-4
Gary1212
Member Posts: 3
in Gas Heating
All lights are rapidly flashing yellow and no zones are working.
Power is good. Gas is fine. Assuming the unit is bad.
The Big Question: How can I bypass the TACO ZVC406-4 unit to allow zones to operate until the unit can be replaced?
If you put a jumper wire from R to W on the t-stat connections does it work?
What type of zone valves do you have?
You should be able to manually open the zone valves and manually enable the boiler to get this running.
A picture of the zone valve and the inside of the controller would help."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
I might suggest checking for a short, zone valve wiring and thermostats. Then check the fuses on the board, there may be spare fuses on the cover as well depending on the manufacture date.0
Thank you for the input everyone. I'm a homeowner with basic 'hanyman' skills and sophisticated electrical is not my specialty. What I'm hoping to find is a way to:
1) Manually open a zone valve (I got that figured out), and;
2) Manually kick the boiler (Weil-McLain GOLD GV) on to provide heat until I can have a PRO come out.
Zman: I've attached pics of what you asked for; any suggestions and/or help much appreciated.0 -
What Zman said. Clean work, nice to see.Steve Minnich0
Zman...Thank you! You are the man; Zman, I mean.0
If all the lights are flashing I would start by first removing thermostat wires (top terminals), one zone at a time to see if that stops it.
If so, you know where to continue looking.
If not, reconnect thermostat wires, and then disconnect zone valve wires, one zone at a time to see if that stops it.There was an error rendering this rich post.
First question, has it worked in the past? New install? or has anything changed if it did work? (sorry bout that, it's actually three)
Dave H.Dave Holdorf
Taco, Inc
- 15.8K Strictly Steam